phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
Is This Answer Correct ? | 2 Yes | 4 No |
How many battery required for an 3kva online ups with 3 hrs back up with usage of 3 fans,3tube lights
what is our body resistance value?
When we getting shock, its we getting from voltage or Current.
Cummins 750 KVA generator how much disel consumed per hour and how many units generated on 100% full load.
If a HV Underground Cable (13.8KV) is layed in the ground below 1.5 Mtrs and any building construction is done on the Cable route. IS this allowable or Not? What should be the clearance. As per ISO construction on HV cable route is safe or Not? Why? Can any body suggest the site for my question?
how to calculate short circuit breaking capacity KA for 2500kva 33kv transformer.
brief notes on ammeters
What will hapen if we connect more capacitors than required for powerfactor control? Exactly what will be the effect on power system?
Can we manually synchronize two DG sets of same ratings manually without using speed biasing ? If yes then how?
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
what collector is used for 100kmph-120kmph tracion application?
Draw torque - speed curve and load curve of induction motor? mark operating point ?