phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
| Is This Answer Correct ? | 2 Yes | 4 No |
What is duty cycle for HT motors? How many start permitted if mentioned as 01 for hot and 02 for cold per duty cycle?
I have two PLC processors. I want to communicate both processor with each other. How i can do so?
1 Answers IHG InterContinental Hotels Group,
What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.
What should be the dielectric strenght value of transformer oil of 11/0.433KV distribution transformer and 33/11KV tranmission transformer ?
Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
what is diffrent between plc and clc??
How to determine stage of Automatic Power factor controlling Relay(Apfcr)?
who is invented transforner (230v).......
HOW TO CALCULATE THE VT SIZING?
what is earth pit , how we can measured it, what earth rods reference
Please let me know DG set b check how many hour and days.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)