phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
| Is This Answer Correct ? | 2 Yes | 4 No |
What is FM200 Fire Supresion System??
IN MY SYSTEM THERE IS ONLY OVER CURRENT EARTH FAULT RELAY IS AVAILABLE. FOR THE UNBALANCE SENSING IS THERE ANY RELAY IS AVAILABLE? THE SAME CTs WHICH ARE USED FOR THE OVER CURRENT EARTH FAULT RELAY CAN USE FOR UNBALANCE ALSO?
What is Form factor?
How RTCC works with OLTC
why we use Bus earth truck and Cable earth truck
why u want to work in sail/ntpc as u r already in an it company where life is good, good environment no much tensions etc?
why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
7 Answers HCIL, Jindal, Siemens,
What are the protections used in a HT breaker to protect the HT motors.
How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors
WHY AIR COMPRESOR IS STARTED UNLOADED
I have doubt that the supply HZ (very low or high than rated ) may affect the power factor. is it true. ?
why using 3 phase
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)