What is the winding resistsnce need to be in a 1000kva,
11kv/415v transformer, between ht winding to lt winding, ht
winding to earth, lt winding to earth.?
Answer / k.prakashchandra
You mean insulation resistance ?As a rough guide,the megger
value should be at least 2 M ohm per KV rating at 60'C for
11 KV and above.The megger value doubles itself for every
10'C fall in temp.
| Is This Answer Correct ? | 1 Yes | 0 No |
What is actual name of Transformer oil.
How does a system control centre in a utility plant gets the grid frequency of the electrical network (50 Hz or 60 Hz)by the SCADA system?
In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?
IF 8255 CONTROL WORD IS 94H,Tell the chip port work mode ?
Where is servomechanism used?
what is draiv work
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
what is the difference between line & phase current in star delta connection motor?
what is full form of lv and mv? 2.while we connect capacitor to generator what will cause for it?
how the speed of the gets motor regulated. does it draw the same current on the all speed level.
WHAT HAPPENED DC SERIES MOTOR FIELD WINDING OPEN. CAN POSSIBLE.
what is POTT and PUTT explain?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)