At what distance power transformer can be placed from
generating ?
Answers were Sorted based on User's Feedback
Answer / rvg.msceb
consider a gen station producing 20MW of power at 11KV. So
current will be 1050 amps. So considering the cabling and
its loss due to heating etc, lowest distance is recommented
from gen stations.preferably less than 100 mtr.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / rod
Any distance, the distance depend on the supply cable size
the bigger the cable the longer the distance, the higher
the voltage also determins the distance.
So the determining factor is to match the cable to the
requirements of the transformer, clearly load and volt drop
is the issue
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / hamed
Any distance and if it is close it is beter due to voltage
drop ,Ohmic losses and cost.
Is This Answer Correct ? | 1 Yes | 2 No |
what is ac servomotor??
explain all the classes with example
Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com
WHAT IS THE SETTING OF OVERLOAD RELAY AND UNDER VOLTAGE RELAY IN PERCENTAGE?
what is meaning of bus riser
What happens if the secondary of the transformer is shorted?
What is servo motor and what are the applications of servo motor?
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
What you have to see in transformer after week, month?
What will happen if 60 Hz rated transformer is connected to the supply of 50 Hz say 415 V (3-phase) step up to 3.3 kV...?? ?
Is it necessary to carry out sheath test after cable jointing? If the value is zero of such instance , is it ok to energize the cable?
hou we find and calculate the maximum lode capesity of transforer?