when we connect the capacitor bank in series
Answers were Sorted based on User's Feedback
Answer / shyamkr
we connect capacitor bank in series to improve the voltage
profile at the load end.in transmission line there is
considerable voltage drop along the transmission line due to
impedance of the line.so in order to bring the voltage at
the load terminals within its limits i.e (+ or - %6 )of the
rated terminal voltage the capacitor bank is used in series.
Is This Answer Correct ? | 5 Yes | 0 No |
Ferranti Effect says that voltage at the receiving end is higher than that at the sending end. How is it possible?
how to test and calculat the head and discharge in borewell compressor
What is the function of trip neutral close switch?
Why usually in all electrical equipment taking more current in Y pahse like pumps,compressor,or any other applications
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
what should be the minimum rating for using HT Motors?
If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.
What is a charge.?
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
cab we add capacitor bank with generator to improve power factor or not??????
define power quality
If single phase voltage level is 230V than why three phase voltage level is not 660V ?, but it is only 440V.