plz tell me about for how many rating (for 500kva)how much
current taken?
Answers were Sorted based on User's Feedback
Answer / vinayak
ans is kva/1.732*volts
so 500kva/1.732*433 volts = 666.66amps on lv side
and 500kva/1.732*11000v= 26.24 amps on hv side
Is This Answer Correct ? | 35 Yes | 1 No |
Answer / mohd mansoor
For 500 kva, It's depend on Voltage,some countryes have
different voltages, according to india,
if ur apply the formula- KVA=1.732x Volt x Amp x 0.8
1kva= 1.39 Amps,
500 kva x 1.39 = 695 Amps.
Is This Answer Correct ? | 48 Yes | 22 No |
Answer / ashish
For 500 KVA Transformer the full load current is 696 Amp.
So we Can Supply the load Upto 696 Amp only....
Is This Answer Correct ? | 31 Yes | 16 No |
Answer / kapil
what is .8 doing in the above formula, while the rating is
given in the KVA and not in Kwatt.
the formula is ..KVA=1.732x Volt x Amp
where voltage will be taken as 415 volt. which is very
common in 3 phase motor rating.
this will produce the same answer as above [695 amps]
Is This Answer Correct ? | 27 Yes | 12 No |
From where you got all these voltage like 440,415,433.
The simple formulae for calculation of current I, if KVA is
given ;
I = (1000 X VA ) / 1.732 x V
So put your available system voltage and get your answer.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / nwachukwu kelechi
The general formula for a 3-phase power transformer is
given by:
power(KVA)=1.732*V*I*pf.
therefore,depending on the pf under consideration, assuming
a unit power factor,500kva power and input voltage of
11000V we have;
current(I1)= 500KVA/(1.732*11000*1)=26.24Amps.
If the output voltage is 400V, the current will then be:
current(I2)= 500KVA/(1.732*400*1)= 721.7Amps.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / senthil kumar.g
1 kva=1.33amps for EB
1kva=1.39amps for DG the varation is bcoz of p.f
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / attique ur rehman
the formula for calculating Single Phase Current is
I = 1000 * KVA/Voltage
Formula for calculating Three Phase Current is
I=1000 * KVA/voltage * 1.732
So for 500KVA we can calculate as below
I= 1000 * 500KVA/440 * 1.732 = 656.6Amps (Depending on
Voltage), if the voltage rating is changed your amps will
automatically change
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / kuttivenu
To calculate the Current
Kva= 1.732*V*I/1000
Ams=696A
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / mohamed ali.m
Formula is here
Example : 500KVA ( 500x 1000) =500000VA
: 500000/415/1.732= 695 Amps
Is This Answer Correct ? | 4 Yes | 4 No |
How to select the rating of the Transformer?
why power not passes in plastic and rubber material
I am working as maintenance engg. in electrical but i want to do carrier in electrical drawing.Tell me about that.
Give me clear explanation.What is the Different Between Load break switch and Vacuum circuit breaker
Why the output of generator varies eventhough the shaft speed is constant in thermal power plant?
Can without battery on line UPS,off line UPS or Invertor works please brief.
how many methods for starting an induction motor?
7 Answers Hindustan Unilever Limited, Hyundai, TPL,
How to obtain B license from TNEB license board. What is eligibility?
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
definition of transformer
This is urgent!! What is a Thyristor-based 3-ways selector switch with Zero crossing control? how does it operate and where is it mostly found in a system?
what is the difference between ac ground and dc ground.. In my project iam using both ac and dc supply.. can both the grounds or the return paths be connected??