The neutral to earth connection in my industry is showing a zero reading
(shorted). I have a machine which has to be installed where neutral to earth is
not shorted and shows a leak voltage <3 Volts. Please suggest me how it is
possible.
Answers were Sorted based on User's Feedback
Answer / bikash
SImple earth is always in zero potential, so when u connect
neutral to earth or measure voltage it will show zero
voltage. But actually neutral is the return path or it is
required for completing a ckt. It shows the unbalaced
system voltage. If system is balaced neutral will show zero
voltage or otherwise it will show voltage. So check load
condition.
| Is This Answer Correct ? | 6 Yes | 1 No |
Hi Ravi
Of course if you have your power supply neutral earthed
from supply side (transformer or generator neutral) you
will get zero potential at between the neutral and earth at
any point of the distribution circuit ; you should get more
information about the type of your earthing system (IT, TT,
TN-S or TNC)
You can find more details at Schneider site or ABB sites
or directly from IEC 60364-5-54 Electrical installations of
buildings - Selection and erection of electrical equipment -
Earthing arrangements
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ravi mittal
The problem has been solved now. I have installed an isolation transformer
which has solved all the issues.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ravi mittal
Dear Bikash,
I am thankful to you for taking interest in answering my
query.
Actually, I have an equipment for which I have been clearly
indicated to not have neautal and earth shorted. If done
so, the equipment may have problems in future. When we
check with the multimeter the neautral to earth is showing
as shorted which gives a zero reading which is actually not
shorted. What can I do in this case where can I either get
a 0 reading (when not short) or <3 volts reading? Is there
a fault with my wiring? Some electricians say that this is
a usual phenomenon in industrial areas. If the phenomenon
is usual, is there a device which can be installed to
rectify this problem.
Thanks and regards,
Ravi Mittal
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kannan
Cheech your earth value as per standard. If not install new
earth rod. It may solve your problem.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / nadir
Possibly your machine required an IT wiring which is unearth neutral. Your machine may required only a PE and the PE electrode shall be installed at a distance of 1.5 longer than your transformer/ neutral earth electrode length.
The isolation transformer will also create harmonics and required to dissipate.
| Is This Answer Correct ? | 0 Yes | 0 No |
apti mainly on logical reasoning, verbal and non-verbal ability (70 percent) and remaining technical. I was in ee but technical had mech ques like on turbines and welding.
Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?
plz tell me in detail about c.t. and p.t. ?
I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly got short what will be the reason.
Does Rheostat can use for power factor correction?
While starting a high capacity motor, it takes 6 times the full load current. Why it doesn't trip relay or CB's in that network?
Explain about retrofitting of machine tool.
From, which load current range ( upper - lower limit current)can Air circuit breaker used for in electrical circuit.
DG B-check,C-Check,D-check is depending upon the running hrs.If the running hrs is not reached as mentioned.How to conduct the DG checks.
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
A 3ph load of 10 KW is equal to how many KW of single phase .
In star and delta connected systems , for driving power and as well as light load which one you will preferred?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)