From, which load current range ( upper - lower limit
current)can Air circuit breaker used for in electrical
circuit.
Answers were Sorted based on User's Feedback
Answer / satya dev ( knight frank)
As per IS- we can use the ACB for 800 Amp.- 4000 Amp.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / kalirajan.n
Gas blast applied on the arc must be able to cool it rapidly
so that gas temperature between the contacts is reduced from
20,000 K to less than 2000 K in a few hundred microseconds,
so that it is able to withstand the transient recovery
voltage that is applied across the contacts after current
interruption. Sulphur hexafluoride is generally used in
present high-voltage circuit-breakers (of rated voltage
higher than 52 kV).
In the 1980s and 1990s, the pressure necessary to blast the
arc was generated mostly by gas heating using arc energy. It
is now possible to use low energy spring-loaded mechanisms
to drive high-voltage circuit-breakers up to 800 kV
| Is This Answer Correct ? | 0 Yes | 1 No |
we can use the air circuit breakers for 2amps upto 2,000
amps.as per the british standard.
| Is This Answer Correct ? | 0 Yes | 1 No |
why generator and t/f ratings given in kva?
HOW MUCH CURRENT DOES SYNCHRONOUS MOTOR TAKES AT SYNCHRONOUS SPEED IN NO LOAD CONDITION ?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
as a electrical student why should i hire you?
From, which load current range ( upper - lower limit current)can Air circuit breaker used for in electrical circuit.
model question paper for supervisor trainee
3) How earthing is done? How it measured? Write the method for earthing? How the earth resistance is kept low?
what is the value will come when megger the phase to phase ,phase to neutral ,phasae to ground ?
what is second harmonic, how is effect transformer ?.
In power plants the reading changes abruptly to give value (MW -25) (MVAR -15) What are the reasons for this? What is the solution?
What is the Designing & Selection Procedure for a DG/Transormer of rated capacity?
How to measure size of cable on a given load
0 Answers Green India Engineering Solutions,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)