While starting a high capacity motor, it takes 6 times the
full load current. Why it doesn't trip relay or CB's in
that network?
Answers were Sorted based on User's Feedback
Answer / a.alexander
Motor Current will take 6 to 7 times for Just 3 to 6 Sec
only. and Cb was with stand the Current in Same Seconds
.That is Set point of CB full load Current.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / blake_australia
The starting current for an induction motor is around 6x
full load current, however this is only for ~3cycles. Which
is about 0.06seconds (for 50Hz power).
Circuit breakers chosen for motors (D curve in Australia)
delay for more than this 0.06seconds. The curves can be
seen in any NHP breaker selection catalog. Protection
curves are more indepth than this, reading into these will
help.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / praful nandankar
Circuit breakers are given sufficient delay time,hence the
relay will not trip when motor takes 6 times the full load
current.
praful nandankar
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sunthosh080
usually when you see the relay technical details there will
CLASS type (5-30)
When your motor is taking 6 times for 5 sec you have to
select 5. So that your relay doesnt trip during this and it
depends on the application also.
If it fan application , then it would be around 15-20.
If the relay is tripping during motor starting then it
CLASS problem.
| Is This Answer Correct ? | 0 Yes | 4 No |
How to check the Bushings of the transformer?
how choose conductor &caple&wire depending upon the load
DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?
what is the formula to find Amp. for an 3 phase moter both if H.P. or if kW is known?
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
Main advantage of auto transformer over two windings transformer is that A it needs no cooling B it uses only one winding C core losses are reduced D it has simple construction
why they were using TRIAC instead relay in some controllers and what is the advantages.
what the reson to use phase shift( angle) like (dyn11,Dd5 or Dy0)are usedin power and transsmison line
How synchronous motor helps to improve PF? plz explain
why we +ve load distribution in 24v and -ve load distribution in 48volt in the telecom sector.?
Why Cables are always circular and not square or rectangular?
How supply comes to your home?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)