While starting a high capacity motor, it takes 6 times the
full load current. Why it doesn't trip relay or CB's in
that network?
Answers were Sorted based on User's Feedback
Answer / a.alexander
Motor Current will take 6 to 7 times for Just 3 to 6 Sec
only. and Cb was with stand the Current in Same Seconds
.That is Set point of CB full load Current.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / blake_australia
The starting current for an induction motor is around 6x
full load current, however this is only for ~3cycles. Which
is about 0.06seconds (for 50Hz power).
Circuit breakers chosen for motors (D curve in Australia)
delay for more than this 0.06seconds. The curves can be
seen in any NHP breaker selection catalog. Protection
curves are more indepth than this, reading into these will
help.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / praful nandankar
Circuit breakers are given sufficient delay time,hence the
relay will not trip when motor takes 6 times the full load
current.
praful nandankar
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sunthosh080
usually when you see the relay technical details there will
CLASS type (5-30)
When your motor is taking 6 times for 5 sec you have to
select 5. So that your relay doesnt trip during this and it
depends on the application also.
If it fan application , then it would be around 15-20.
If the relay is tripping during motor starting then it
CLASS problem.
| Is This Answer Correct ? | 0 Yes | 4 No |
why we are using KVA rating for transformer,not KWh rating?
what is earthing
If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive
What is I to C?
Why is it that polarization index type test is required for MV and HV motors and not for LV motors?
3 Answers La-Gajjar Machineries, Qatar Airlines,
Is AC Current Scalar or Vector Component?
where is the need for short circuit test for 3 see is required and why? can you explain in brief with application
what r Grid stations?what r there role.Explain in detail
why it is unable to birds to be on a 220kV 0r 132 kv lines like on 33kV and 11kV lines?
4 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB
why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)