Answer / ran7it
u can use a hipot kit. for a 33kv cable the voltage 2 b
applied can b determined by formula (2E + 1),,whr E is the
system voltage,so for tis case it comes as 2*33 +1=67kv.
tis 67kv is mostly applied for the first time in factory
testing..after tat only 60-70% of 67kv sud b applied.
the cable has to withstand tis voltage for 1min..
| Is This Answer Correct ? | 27 Yes | 4 No |
Answer / rod
Answer 5 is correct, the only thing is it is now not common
practice to Hi-pot cables as this can cause damage to it,
PD tests is the normal method of testing.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / john sundararaj
First decide on which type of cable
type of insulation,single core or 3 core
Ans 8 is the right one.Always go by the manufacturers
recommendation.The values differs for each standards and varies for different countries/utilities.Most of them prefer
soak test rather than hipot.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mc
we have to consider the phase voltage to ground and nature
of material, but for the first test it's every time
manufacture specification as to be follow.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh babu
HI POT test how much KV applied for 33KV Cable and Time
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s bhattacharya
TO DECIDE THE VOLTAGE APPLICABLE FIRST THING TO SPECIFY
TYPE OF CABLE .
1.IF SINGLE CORE 9NEW CABLE)THEN AS PER IEC GO FOR
BILX0.8/1.732 -AC WITH VARIABLE FREQUENCY CONTROL KIT TO
ADJUST THE FREQUENCY AS PER CABLE LENGTH.
FOR CABLES LESS THAN 132kV.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / guest
Cables are naturally made of pvc,so we can apply high
voltage test to the cables and if its in no damage in high
voltage it should be declared good cable.
| Is This Answer Correct ? | 8 Yes | 14 No |
Answer / blake australia
A lot of HV cables are XLPE not PVC. If you Megger a 33kV
cable with a DC voltage then you may damage the XLPE
semiconductor around the cable.
Industry standard in Australia(although very expensive to
buy one) is to use a VLF (very low frequency) tester to
test the cables. Same principal as mentioned, just uses an
AC waveform (~.1Hz) opposed to a DC waveform.
| Is This Answer Correct ? | 5 Yes | 14 No |
how to produsing geretor power
A ii kv 1200 A Breaker combination fixed in a cubicle. How many ampere Fuse is required? If fuse is not using, Why?
if transformer core is made of copper instead of steel which losses will increase..please explain
what should be the acceptrd value of winding resistance for 2.5MVA transformer
how to select cable size?
why can the rotor of 3 phase slip ring induction motor not be a 2 phase rotor?
definition of fault level in powersystems?
what is the speed of current?
what is frequency response?
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
what happen ,if generator will generate leading power factor?
Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)