Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV
CABLES.EXPLAIN IN DETAIL

Answers were Sorted based on User's Feedback



WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / ran7it

u can use a hipot kit. for a 33kv cable the voltage 2 b
applied can b determined by formula (2E + 1),,whr E is the
system voltage,so for tis case it comes as 2*33 +1=67kv.
tis 67kv is mostly applied for the first time in factory
testing..after tat only 60-70% of 67kv sud b applied.
the cable has to withstand tis voltage for 1min..

Is This Answer Correct ?    27 Yes 4 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / pracash

45KV voltage must be applied

Is This Answer Correct ?    13 Yes 8 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / prashant

answer 5 is correct

Is This Answer Correct ?    7 Yes 2 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / rod

Answer 5 is correct, the only thing is it is now not common
practice to Hi-pot cables as this can cause damage to it,
PD tests is the normal method of testing.

Is This Answer Correct ?    7 Yes 3 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / john sundararaj

First decide on which type of cable
type of insulation,single core or 3 core
Ans 8 is the right one.Always go by the manufacturers
recommendation.The values differs for each standards and varies for different countries/utilities.Most of them prefer
soak test rather than hipot.

Is This Answer Correct ?    3 Yes 0 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / mc

we have to consider the phase voltage to ground and nature
of material, but for the first test it's every time
manufacture specification as to be follow.

Is This Answer Correct ?    0 Yes 0 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / suresh babu

HI POT test how much KV applied for 33KV Cable and Time

Is This Answer Correct ?    0 Yes 0 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / s bhattacharya

TO DECIDE THE VOLTAGE APPLICABLE FIRST THING TO SPECIFY
TYPE OF CABLE .
1.IF SINGLE CORE 9NEW CABLE)THEN AS PER IEC GO FOR
BILX0.8/1.732 -AC WITH VARIABLE FREQUENCY CONTROL KIT TO
ADJUST THE FREQUENCY AS PER CABLE LENGTH.
FOR CABLES LESS THAN 132kV.

Is This Answer Correct ?    3 Yes 4 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / guest

Cables are naturally made of pvc,so we can apply high
voltage test to the cables and if its in no damage in high
voltage it should be declared good cable.

Is This Answer Correct ?    8 Yes 14 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / blake australia

A lot of HV cables are XLPE not PVC. If you Megger a 33kV
cable with a DC voltage then you may damage the XLPE
semiconductor around the cable.
Industry standard in Australia(although very expensive to
buy one) is to use a VLF (very low frequency) tester to
test the cables. Same principal as mentioned, just uses an
AC waveform (~.1Hz) opposed to a DC waveform.

Is This Answer Correct ?    5 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

how to produsing geretor power

0 Answers  


A ii kv 1200 A Breaker combination fixed in a cubicle. How many ampere Fuse is required? If fuse is not using, Why?

0 Answers  


if transformer core is made of copper instead of steel which losses will increase..please explain

5 Answers   Bhel,


what should be the acceptrd value of winding resistance for 2.5MVA transformer

0 Answers  


how to select cable size?

7 Answers  


why can the rotor of 3 phase slip ring induction motor not be a 2 phase rotor?

0 Answers  


definition of fault level in powersystems?

4 Answers  


what is the speed of current?

29 Answers   Su Kam, TATA,


what is frequency response?

0 Answers  


in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.

1 Answers   Gasal, Voltech,


what happen ,if generator will generate leading power factor?

6 Answers   CD, NTPC,


Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)