Answer / ran7it
u can use a hipot kit. for a 33kv cable the voltage 2 b
applied can b determined by formula (2E + 1),,whr E is the
system voltage,so for tis case it comes as 2*33 +1=67kv.
tis 67kv is mostly applied for the first time in factory
testing..after tat only 60-70% of 67kv sud b applied.
the cable has to withstand tis voltage for 1min..
| Is This Answer Correct ? | 27 Yes | 4 No |
Answer / rod
Answer 5 is correct, the only thing is it is now not common
practice to Hi-pot cables as this can cause damage to it,
PD tests is the normal method of testing.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / john sundararaj
First decide on which type of cable
type of insulation,single core or 3 core
Ans 8 is the right one.Always go by the manufacturers
recommendation.The values differs for each standards and varies for different countries/utilities.Most of them prefer
soak test rather than hipot.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mc
we have to consider the phase voltage to ground and nature
of material, but for the first test it's every time
manufacture specification as to be follow.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh babu
HI POT test how much KV applied for 33KV Cable and Time
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s bhattacharya
TO DECIDE THE VOLTAGE APPLICABLE FIRST THING TO SPECIFY
TYPE OF CABLE .
1.IF SINGLE CORE 9NEW CABLE)THEN AS PER IEC GO FOR
BILX0.8/1.732 -AC WITH VARIABLE FREQUENCY CONTROL KIT TO
ADJUST THE FREQUENCY AS PER CABLE LENGTH.
FOR CABLES LESS THAN 132kV.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / guest
Cables are naturally made of pvc,so we can apply high
voltage test to the cables and if its in no damage in high
voltage it should be declared good cable.
| Is This Answer Correct ? | 8 Yes | 14 No |
Answer / blake australia
A lot of HV cables are XLPE not PVC. If you Megger a 33kV
cable with a DC voltage then you may damage the XLPE
semiconductor around the cable.
Industry standard in Australia(although very expensive to
buy one) is to use a VLF (very low frequency) tester to
test the cables. Same principal as mentioned, just uses an
AC waveform (~.1Hz) opposed to a DC waveform.
| Is This Answer Correct ? | 5 Yes | 14 No |
WHAT SHOULD BE THE RATING OF generator required to run a pump motor of 45 Kw.
what is the principle of switch gear? where its function ?
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
As per BIS, Earth pit resistence value?
What is resistance of 50meters, 16sq.mm, single core copper cable?
1 Ton is equal to how many watts?
Why the motor take high starting current for long time(10- 15 sec) which is connected to Blower as compaire with a motor which is connected with pump with same rating?
What are all present producing cost of Per KWH of various Fuel?
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES ?
KVAR Kilovolt-Ampere-Reactance
why fan consume constant power even when we increase or decrease its circuit resistance through speed regulator???
why the 4 terminal are named as main, line, common, voltage (M, L, C, v) of a wattmeter?? why not its nameed as A,B,C,D??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)