Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV
CABLES.EXPLAIN IN DETAIL

Answers were Sorted based on User's Feedback



WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / yasar

to test hipot with vlf the applied voltage must be as follows
33/1.732=19.0,this is the individual RMS phase to ground
voltage of one phase,this voltage must be multiplied three
times for three phases which gives you 57.1KV.

Is This Answer Correct ?    5 Yes 14 No

WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL..

Answer / ashish

For 33 KV Voltage Cable 33000*1.732 DC Volt We Have to
Apply........

Is This Answer Correct ?    4 Yes 15 No

Post New Answer

More Electrical Engineering Interview Questions

How to checking sld drawingas and control drawings

1 Answers  


HOW TO TEST A LIGHTENING ARREST ER ?

0 Answers   Bhushan Power Steel,


On what basis do you decide the ONAN (Oil Natural air natural) or Dry type transformer for a project?

0 Answers   Semac,


how many power plants in andhra pradesh,how many types and there capacity

2 Answers  


(1) From the following option, which option is correct for largest size transformer.? a)1KVA,25Hz , b)1KVA,50HZ , c)1KVA,60Hz , d)1KVA,100Hz

5 Answers   Torrent Power,


What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?

0 Answers  


how can you size an automatic voltage regulator?

0 Answers  


If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?

2 Answers   ABB, Unitech,


Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer

2 Answers  


WHY ARE THE LT GENERATORS SOLIDLY EARTHED WHILE THE HT GENERATORS ARE EARTHE THROUGH NGR OR NGT??

3 Answers  


how the speed decreases of a generator in power station if load increases

1 Answers   Tata Power,


where connected OLTC for transformers?

3 Answers   Apollo, CBRE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)