how the calculation is done if the DG set require for the --
-48 to -51v 4000 ah battery set .
Answer / k.prakashchandra
Generally ,the charging rate should be at least 10 % of AH
of the battery set numerically,so that full charging time
will not exceed 10 hours.
| Is This Answer Correct ? | 2 Yes | 0 No |
what curve and rateing would you use for a three phase 0.75kw motor?
21. What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing? 22. What are the protections to be used for Generator? 23. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0 24. What happens when the polarity changes in CT? Explain briefly? 25. Explain the Term in CT Name Plate – Class: 5P10
What is difference between metal clad & metal enclosed switchgear?
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?
What is the difference between Isolator annd Circuit Breaker.
21 Answers ABB, Lanco, NTPC, Power Grid, RInfra,
what is the maximum load in MDB,SMDB and DB
why the efficiency of generator is more than the motor in case of swinburne's test????
State kirchoff current law?
What kinds of decision are made about CT from it's Knee point(voltage & current)?
what is the d/f b/w iverter & converter.
How to work meggar?
what happens when we give supply to the secondary of a transformer ?? for example 415v(pri)/110v(sec)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)