Answer / venkat iyer
Selection of CTs depends upon its usage, whether for
metering or protection. Class of accuracy, VA burden and
palatability to instrument safety factors need to be
considered incase of metering CTs. In case of protection
CTs, linearity factor w.r.t its primary current and
accuracy factors need to be considered. Metering CTs are
expressed in terms of Class 1 or Class 3 where as
protection cts are expressed as 5P10 or 5P15 or 5P20 or
10P10 etc. The first digit stands for the class of accuracy
and P stands for protection and the last two digits stands
for linearity.
| Is This Answer Correct ? | 44 Yes | 0 No |
Answer / mervin
A CT used for Instrumentation is required to be accurate
over a normal working range , whereas CT for protection is
required to five a correct CT ratio several times the rated
current . Cores made using Nicel-Iron alloy gives accuracy
upto 5 times the rated current n suitable for
Instrumentation . Cores made using Cold rolled silicon
steel are accurate upto 15 times the rated current and
suitable for protection .An accuracy of about 2-3% is
desirable for distance and differential relays .CT burden
and CT linearity should also be considered during selection
of a CT .
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ramakrishna m
The selection of CT depends on the current ratings of relays
those are used in the protecting circuitry and also depends
on accuracy that circuitry requires.
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / kapil
it depends on the protection circuitary ratings and the
accuracy u desire for the application. it must supply the
rated current to the relays with the accuracy u desire for
ur purpose,and also copper losses in the CTs should be
minimum so it also depends on the laminations and conductor
material u choose.
| Is This Answer Correct ? | 3 Yes | 8 No |
i wanna know that star point in transformer becomes as a neutral on secondary side now tell me that how is that possible?because if joit the all three winding ends with each other it can b short circuited.dut it doesn't.WHY?pls Answer me in brief.thanks alot
What are the safeties in elevators?what is the use of governor in elevator?
What is The Resistance Formula
Mention the value of earth resistance and factors on which it depends on.
what is working parincipal of a ht transformer
what is interference
different between horse power and break horse power
When a fourth resistor is connected in series with three resistors, the total resistance
How will you utilise electrical power? You can start from the generating station.
Electricity sometimes can be dangers , sometime got shoked form it . It is because of volatge or Current
Can u start a tube light without a starter?
What happent when a AC motor(no break and starters ) stop and suddenly start . ? Starting current low or high?? Why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)