in dc shunt generator field is open in running condition
what will happen?
Answers were Sorted based on User's Feedback
Answer / ravi693
If field of DC Shunt generator will opened then generated
voltage will reduced to 2 or 3 volts.
| Is This Answer Correct ? | 16 Yes | 4 No |
Answer / v.karthikeyan
If the sunt field of the Generator got opened the Back EMF
will be drastically reduced and there will not be flux
linkage between the armature field and sunt field.Hence
output voltage will not be as sufficient as stipulated.
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / j.d
if the field winding of the shunt generator gets open then the generating voltage gets reduced to very low level finally it gets zero output from the generator, because field winding is the main element to produce flux. The flux is directly proportional to the output voltage.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / hskk
if in dc generator field is open the flux will be zero and
as speed is inversly proportional ti flux the speed will be
infinite theoretically. it means practically the speed will
so high that it will damage the machine
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / vilas
In dc shunt generator if the field is open in running
ondition the generators speed will increase,definately,but
in practical there some protection, as a field failure
relay,it will operate and stop the generator.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / lavakumar
As the speed is inversely proportional to flux,as field is
removed,speed is said to increase theoritically but
practically the speed enourmously increases which may
damage the generator.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / v.selvakumar
n=emf/flux according to this formula field open means flux
will be zero.flux zero means speed will be infinity,but we
know that no machine can't reach infinite speed.so that
therotically ok but practically starting speed will
increase then it will reduced zero.
| Is This Answer Correct ? | 3 Yes | 11 No |
Answer / nimish
if the field of dc shunt generator is open the speed of the
generator will be infinite and it will damage.
| Is This Answer Correct ? | 7 Yes | 16 No |
explain transformer ct connection?
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
why the flooring of substation is done with small pebbles or stones..?
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
how we select the fuse and OLR rating for 3 phase induction motor from 1HP TO 100 HP?
how much load 15kva dg set can bear
HOW SKIN EFFECT REDUCE THE CROSS SECTION OF THE CONDUCTOR
what is the function of commutator in dc motor?
if you short the any 2phase(R,Y,B),why fuse get blown?
what is TPN
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)