Why transformer is rated in kva?
Answers were Sorted based on User's Feedback
Answer / himadri bag
Rated transformer output is limited by heating and losses. There are two types of losses core loss and ohomic loss. Core loss depend on voltage(V) and ohomic loss depend on current(I)
and almost unaffected by the load power factor(pf). That is why rated output expressed in VA or kVA(V*I) not in KW(V*I*pf).
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / himadri bag
rated output depends only current and voltage not in the power factor. so the transformer is rated in VA or kVA(V*I) not in kW(V*I*pf)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / surya pratap singh
because the losses of transformer is no depend on the power
factor and its power factor is depend on self so the rating
of transformer is kva.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / lokesh kumar raman
the transformer devloped two type of losses first eddy current loss it depand of current and second is hystrisis loss it depand of voltage .so we are taking rating of transformer in kva.
| Is This Answer Correct ? | 0 Yes | 1 No |
i want to know that what is the eligibility critaria for ongc exam?
In liquid rotor starter how PH valve should be maintained.
Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?
how is motorized megger operate?
Differentiate AC and Dc resistance
How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size of cable is used for this motor.
how we calculate electrical load on a building according to area?
What is the difference between KW & KVA ?
Good morning: I'm looking for some informations about the OLTC or the LTC: I wont to know what the function of the tie-resistor in during the operation of reversing/coarse operation Cordially
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
Whether the Dc motor Droping the power factor like AC motor if lot of motor running in factory is it necessary to connect capacitor bank
what is meant by 3rd hormonics ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)