If the supply voltage is same (say 440V) whether a system
designed for 60 Hz frequency will work with 50 Hz frequency
or not , if so pl. give clarification.
Answers were Sorted based on User's Feedback
Answer / joysbag@gmail.com
E=4.44(freq.)x(fluux density).
if E is constant - freq is inversly proportional to Flus
density.
Hence with 10% decrease in freq the flux density will
increase by 10% which may bring the transformer at
saturation. Hence it may work but not advisable.
Is This Answer Correct ? | 11 Yes | 1 No |
Dear all I've seen that all r telling dc motor, ac motor,
converter etc. ABB has asked for a system not for motor/
inverter. As the equaiton of joysbag reduction of frequency
of 10% will cause increment of 16.67% of flux. Though the
system is designed about 60Hz. Then the system component
may be malfunctioning. All of equipments of the system must
be changed as frequency has changed.....
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / sanjeev kumar
yes system will work with unproper way but the system are
designed as per basic parametre like frequency, voltage,
current,. if we changed the parametre system work with
abnormal way.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maheswaran
iron losses such as hysteresis and eddy current losses are
proportional to the frequency of the supply.. so the
frequency increases,obviously losses will increase
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rameshpaulaian
Its work both 50Hz and 60Hz , but the output is diff from
each.
Ex: Fan, Speed of fan at 60Hz< Speed of Fan at 50Hz.
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / glen saldanha
definately the electronic appliance such a tv will not work
as the calculation of capacitor and inductor rating is
based on 50hz changing the frequnecy to 60 hz will change
the valve and the electronic appliance will behave abnormal
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / naveen
it depends on the application, each eqipment is allowed for
some variation in the parametr. For Ex in case of induction
motor upto 5% variation is allowed in the frequency.So the
behavior of system depends on how much sensitive to that
parameter.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tarun aggarwal ymca
actually certain equipment work on the frequency of power
supply such as oscillators or frequency changer used to
trigger the ckt . since frequency has been changed the
resulatnt triggering angle get chandged which offer un
predictable result .
while if a d.c motor is given 50 Hz it commutation process
is designed in such a way that is frequency increase it will
led to short circuiting
Is This Answer Correct ? | 1 Yes | 4 No |
what is the cable capacity of any load wise .
which one is more costly:single phase induction motor or 3 phase induction motor??give proper reasons..
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
full form of electrical?
why power factor is only cosine angle not sine angle?
why the desirable efficiency for a motor is 60%, but in case of transformer, it is above 90%?
what is the purpose of reactor in electrical substations ?
why HT line voltage is multiple of 11.eg11kva,33kva,132kva
What is notching in dc machine?
FOR ELECTRICAL TRANSMISSION TOWER WHAT SHOULD BE THE MINIMUM HEIGHT FROM THE GROUND? AND WHAT SHOULD BE THE DISTANCE BETWEEN THE TWO CONDUCTOR?
what is difference between neutral& grounding?
I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila