how to connect generators in parallel and what are the
required equipment to do so?
Answers were Sorted based on User's Feedback
Answer / paramesh
for the two generators connected in parallel by following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,synchronuscope will be
used.
Is This Answer Correct ? | 20 Yes | 0 No |
Answer / bijulal
for the two generators connected in parallel the following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,wattmeter,
synchronuscope& reverse current relay will be
used.
Is This Answer Correct ? | 10 Yes | 3 No |
A mass of 1200g is accelerated at 200 cm/s2by a force. The value of the force required is:(a) 2.4N(b) 2400N(c) 240 kN(d) 0.24N
how can we check a fully charged battery?
6 Answers BEML, Singareni Collieries,
Which one is correct mVA or MVA. Whether both the units are same for the transformer
what happens if you swap F1 and F2 connection in the exiter of the generator?
Why Power generation in India is at 50Hz while in America its 60Hz so is there any advantage/Disadvantage of this ??
38 Answers Australia Visa, College School Exams Tests, Fiat, InfoPlus, L&T, NTPC, TCS,
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
What do you mean by boost voltage in case of battery charger?
why asa method ZPF method is more accurate than ASA method?
in transformers for ex. 100mva and 400kv the secondary current is about 420 amps but for selection of bushing the capacity of selected bushing is 2000A why there is such big difference ?
what is frequency? and its importance
Where there is voltage,there must be current.Is this right or wrong??
differance b|w ground, neutral&earth