How can we calculate the rating of a transformer suppose if
load is 1000KW?Formula?
Answers were Sorted based on User's Feedback
Answer / anil dhakar
We know that
KVA=KW/POWER
FACTOR. If the
p.f. is not
given we takes
0.85 value of
p.f.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / proshant
We can dtermine the rating of transformer by multiplying the
power that given inreal power with the power facor.If
thepower factor is not given,then we can imagine it as 0.85
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
The pf is not to go below 0.85 and loading factor can be
taken as 0.9 or as low as 0.7 in anticipation of future
load.Then 1000/ 0.85 x o.9 or 0.7 i.e. 1300 KVA or 1700
KVA is the required rating.
Is This Answer Correct ? | 0 Yes | 0 No |