what happens when d cexcitation given to alternator is
removed while it is running or what happens when dc
excitation is failed in alternator while running?
Answers were Sorted based on User's Feedback
in this case alternator wil work as induction generator, as
reactive power supplied by AVR wil be zero due to loss of
excitation, generator wil be in asynchronous mode.
Is This Answer Correct ? | 48 Yes | 9 No |
when excitation is lost due to fault or field breaker
tripping . Reactive power will be supplied by the system and
generator will work as induction generator and its speed
will rise a little . generator which was in over excitation
mode will work in underexcitation .
but there is under excitation limit which should not be
reached so we should detect loss of excitation and trip
generator
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / sunil kumar
when the excitation is lost,alternator tends to behave as
induction generator because there is no opposition to the
rotor as flux is zero, rotor speed tends to increase beyond
synchronous speed and by reactive power from the grid the
machine behaves as induction generator as slip is negative
and reverse power flows which will be taken care by
directional relay.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / nishad
Generator will not produce any output voltage and it will trip the generator output breaker by the loss of excitation monitor protection relay or under voltage relay. If the breaker not trips by these relay, it will trip by reverse power relay. Due to the presents of Reverse Power relay, it will not allow the Generator to run as an induction generator and will trip the Generator breaker, thus it protect the generator from further severe fault. Again, if it not trips by these all protections, alternator will work as induction generator due to the residual magnetism in the field core when it is running in parallel and it will give the over load to another generator as a result, it will trip entire system. Also, as an alternator typically isn't designed to operate as an induction machine, the windings on these machines will heat up and damage. Therefore, need to make sure the reliability of protection relays to avoid such faults.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / atul
if excitation fails let d case of hydro generator the prime
mover is turbine. since turbine ic moving and is coupled
with generator shaft and no flux to control its speed it
will go out of path or speed will increase beyond
synchronism
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / ramlakhan y adav (ballia)
when the excitation is removed then the alternator work as a
asynchronous motor will draw the power from reverse supply.
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / manjeet
duction generator as underexcitation .
but there is under excitation limit which should slip is
negative
and reverse power flows which will be taken care by
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Every one is right but one more thing will happen that is
Alternator will work like motor and will draw power from
other source ( with that it synchronised )known as reverse
power and further RPR will trip the Alternator breaker.
(Approx continuous rating for reverse/negative power is 10%)
Is This Answer Correct ? | 7 Yes | 14 No |
Answer / vijin
if the excitation fails the motor will simply stops,because
it loses the magnetic locking capability by the removal of
dc supply. the motor has no field suplly to generate
necessary emf while running by virtue of the inertia.
Is This Answer Correct ? | 3 Yes | 14 No |
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
I have 30KW Motor Starter Panel, System voltage is 480V, So i have to convert voltage 480 to 220V to give the contactor coil. How i can select control transformer, Which rating transformer i can use this panel, what is the procedure, please tell me.
why we r used DC megger insted of AC megger?
if i am in front of transmission line how to know that current direction without any equipment
why we use to always generate power below 16kv.why not at higher voltage?
What is meant by cold loop test in instrument
does any one know where we can purchase insulation oil for high voltage oil filled cables
hi, i finished b.tech eee in 2008, im worked in dg sets mfg company , now i left job in 6months back, now again i want get job core side, how can i get? is there any couses we have learn to get better oppurtunity? /
If one lamp connects between two phases it will glow or not?
What is frantic effect?
when we connect the capacitor bank in series
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?