how we have to calculate the short circuit current for
33/11kv 2mva, 7.5% Z, Transformer primary side breaker and
secondary side breaker short circuit current for both sides?.
Answers were Sorted based on User's Feedback
Answer / sunil ulange hit nidasohi
Sort circuit MVA= Rating * 100 / Z%
Short Circuit Current =Short circuit MVA / 1.732* Voltage
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / karuppannasamy
Rated primary current=2000/(1.732*33)=35A
Short circuit current= Rated current/Impedance
= 35/.075=466A
Similarly
Rated secondary current=2000/(1.732*11)=105A
Short circuit current=105/.075=1400A
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / madhu
Fault impedance in secondary Z = %Z x 10 x (KV)²/KVA
= 7.5*10*11*11/2000
= 4.5 OHMS
then fault current in sec = V/(Z*1.732)
= 11000/(4.5*1.732)
= 1411 A or 1.4kA
similarly in primary Z = 7.5*10*33*33/2000
= 40.83
then fault current in prim = 33000/(40.53*1.732)
= 0.466kA
| Is This Answer Correct ? | 0 Yes | 3 No |
What is a roll of a adopter pannel in buscoupler pannel????
What is A.C Resistance for Earthing ?
What is the meaning of In,Io & Ir in Circuit breaker? How to calculate?
if a single phase 3 hp submersible pump of Crompton Greaves is moving in reverse direction and sometimes it moves in rigth direction ,then what may be the cause....
what is subtransient , transient and steady stateac components
Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..
why bulbs when connected in series glow dim
Can u explain : how capacitor act when the supply is given is a.c and d.c. I know that when d.c supply is given then the capacitor charges and becomes open circuited. But please say about when a.c is given. I have seen that when a.c supply is given ,it charges and discharges, But when we plug in capacitor to our daily supply and take it out ,then we join those wires spark will appear,which seems charge is present ,but when a.c is given it should charge and discharge
what is the difference between cable routing and scheduling?
If ac voltage applied to the field of dc generrator the output of dc generator ?
What are steps to be taken while designing of DYN11 distribution transformer to achieve magnetising balance?
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)