how we have to calculate the short circuit current for
33/11kv 2mva, 7.5% Z, Transformer primary side breaker and
secondary side breaker short circuit current for both sides?.
Answers were Sorted based on User's Feedback
Answer / sunil ulange hit nidasohi
Sort circuit MVA= Rating * 100 / Z%
Short Circuit Current =Short circuit MVA / 1.732* Voltage
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / karuppannasamy
Rated primary current=2000/(1.732*33)=35A
Short circuit current= Rated current/Impedance
= 35/.075=466A
Similarly
Rated secondary current=2000/(1.732*11)=105A
Short circuit current=105/.075=1400A
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / madhu
Fault impedance in secondary Z = %Z x 10 x (KV)²/KVA
= 7.5*10*11*11/2000
= 4.5 OHMS
then fault current in sec = V/(Z*1.732)
= 11000/(4.5*1.732)
= 1411 A or 1.4kA
similarly in primary Z = 7.5*10*33*33/2000
= 40.83
then fault current in prim = 33000/(40.53*1.732)
= 0.466kA
Is This Answer Correct ? | 0 Yes | 3 No |
What is a doble test
1 Answers KPSC Karnataka Public Service Corporation,
Why the efficiency of generator is more than motor in swinburne's test
How many devices can be connected in one zone of FACP
what is humming noise and wha is the reason to develop humming noise in a mv pannel ?
why normally Generator rating are between 11Kv to 22Kv?
How does a diesel generator works?
What is transient Phenomenon?
what are smoke detectors ?
4 Answers Indian Military Services,
definition of fault level in powersystems?
At what speed 1 HP motor can run an electric car of weighing 400 kg?
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
What happen when switch yard one pole not tripe when you tripping the breaker