How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answers were Sorted based on User's Feedback
Answer / imran mazhar
You did not say what efficiency, whether you get good KWH/
diesel consumption or whether the genset is loaded
efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION
METER.If you run your 1000KVA gen set for 20 hrs.your
genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If
YOUR KWH generated reading says 12000kwh than your
generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate
seperately for both of them.
| Is This Answer Correct ? | 18 Yes | 27 No |
what is feed back and what are feed back amplifiers?
How to calculated capacitor rating both HT
differentiate between c curve and d curve MCBS?
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
what is the function of choke in a tubelight
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
what is the voltage present in the telephone?
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a campus site?
why are distributed windings generally used in alternators?
what is the meaning of the parameters labeled on the surge arrestor like 150/20 ???
We have a 62.5 KVA DG with Leyland engine and kirloskar slipring alternator. We have earthed the neutral, and another earthing for the dg body. is it necessary to isolate the dg foundation with rubber pads?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)