How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answers were Sorted based on User's Feedback
Answer / imran mazhar
You did not say what efficiency, whether you get good KWH/
diesel consumption or whether the genset is loaded
efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION
METER.If you run your 1000KVA gen set for 20 hrs.your
genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If
YOUR KWH generated reading says 12000kwh than your
generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate
seperately for both of them.
| Is This Answer Correct ? | 18 Yes | 27 No |
Why RCD trips on connecting to one Socket but not trips one other circuit on same RCD.
Is a d.c.compound motor is use as a booster? how?
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current ?
What is Harmonics how it is produced and what is the method to control the same
What is class ab operation?
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
Whata are the types of Cables?
standard earthing rating for power line..
when we change tha taps from 1-16 in 100mva tr whether a constant voltage avaliable till it reaches tap 16 or voltage change as per taps change
what happens in a genarator when rotor supplied with ac instead of dc
why we use 6nos of C.Ts on 11kv incoming?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)