Answer / ashli
when a motor rotates a back emf(E) is induced in the
armature which will oppose the supply voltage(V).. E is
proportional to the speed ie at zero speed there ll be no
back emf.. the current thro' the armature is (V-E)/R; where
R is the armature winding resistance(small value). at the
instant of starting speed is zero and so the value of E.
thus the current = V/R becomes very high.. once it attain
speed E is generated and current falls down
Is This Answer Correct ? | 39 Yes | 3 No |
Answer / prakash suhane
During start motor requires high torque to get rated speed.
Requirement of high starting torque leads to large back
E.M.F and t6o overcome this back EMF high current flows
during starting of motor. once motor reached its rated
speed current reduced as per load current on motor.
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / rambabu
During start motor requires high torque to get stating load
is zero.also this will given lower o/p voltege per RPM.but a
higher current per phase
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / chreamz
During starting time, the motor acts like a blocked rotor.
The flux created on the armature turn to oppose that of the
rotor. Hence the motor amperage rises far beyond the
rating. It's estimated that, during starting time of the
motor, Operating Current = 6 times Norminal Current.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the general power factor & min. power rating of TV,LCD type TV, CRt type TV, Scanner, printer?
i need mat lab program to find out the transmission line losses,regulation and losses
mention hazard experienced during installation
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
what is the basic principle of TV camera?
Why Lead-Acid cell voltage is 2.1 volt, why we can not chenged it cell voltage by using extra row-material, only incries its AH.
What is notching in dc machine?
I know the Capacitor value- 12.5KVAR, voltage 440V gas filled, then what is the formula for calculate the microfarad value for this 12.5KVAR capacitor
which meter used to measure a flus
how is calculated the quantity of weight in hot test xlpe?
What is the difference between online and offline UPS