What will be the full load current of 60KVA UPS. Suggest
for this formula.
Answers were Sorted based on User's Feedback
Answer / sujit288
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
| Is This Answer Correct ? | 71 Yes | 8 No |
Answer / muralidhar k.s
Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva
Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / sreenu
Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.
So I(Current)= S (Apperent power)/Voltage only.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / guru
i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / murugesh.k
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kumar
formula of 3 phase power calculation
p=1.732*VL*IL*cos@
60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS
| Is This Answer Correct ? | 9 Yes | 11 No |
how can we calculate the ampacity of the electrical wire/cable. and what are the factors must be considered. pls. elaborate.
Everybody Knows What is ACB, VCB but anybody tell me what is ST?
power 148kw i need exat cable size in 148 kw in 3phase what size of cable can i used.
When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.
Do closed loops systems require manual input?
How to know Resistance and Reactance value of main and aux winding of single phase capacitor start capacitor run induction motor to find capacitor value?
A 3ph load of 10 KW is equal to how many KW of single phase .
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
what is ICU and ICS in breaker ratings
Can we use shunt trip coil instead of trip coil with protection relay for protection?
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
when the control mechanism is present for an ammeter(1-10A) and 1A current is apllied what will be the reading of the meter?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)