What will be the full load current of 60KVA UPS. Suggest
for this formula.
Answers were Sorted based on User's Feedback
Answer / sujit288
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
Is This Answer Correct ? | 71 Yes | 8 No |
Answer / muralidhar k.s
Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva
Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.
Is This Answer Correct ? | 23 Yes | 1 No |
Answer / sreenu
Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.
So I(Current)= S (Apperent power)/Voltage only.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / guru
i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / murugesh.k
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kumar
formula of 3 phase power calculation
p=1.732*VL*IL*cos@
60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS
Is This Answer Correct ? | 9 Yes | 11 No |
What is distance between electrical panel to land ?
What is the value of system voltage?
determine two methods to find loose connection in operational electrical system?
Hi guys! Plz help me to answer the following questions. 1. What are the types of transmission line energy losses? 2. Why are the VLF are used some types of services? 3. What frequencies are used for reliable beyond the horizon terrestrial communication without repeaters? 4. To permit selection of 1 out 16 equi-probable, what is the number of bitis required? 5. What is the most common modulation used for telegraphy? 6. What is the multiplexing is used to increase the capacity of the optic fiber? Thanks
When we use PT in HT Panel why the ratio is 11Kv/√3/110v/√3 please explain briefly with suitable formula?
what is trip circuit supervision relay? How does it work in switchgear?
6 Answers Radha Regent Hotels,
formula for cable size calculation for current?
10 Answers KL Power, ONGC, RL Clean Power Pvt Ltd RLCPPL, SAS, Sobha Developers,
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
What is a variable speed motor?
Pls tell me whether we can use EN3A material for shafts of Permanent magnet alternator.What will be the effect of magnetic and nonmagnetic material for shafts on magnetic properties of PM rotor .
In Generator How suction compression power and exhaust works ?
what happens if we earth negative electrode of an rectifier transformer used in ESP. In which normaly positive is earthd from inside the xmer.