Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What will be the full load current of 60KVA UPS. Suggest
for this formula.

Answers were Sorted based on User's Feedback



What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sujit288

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    71 Yes 8 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / muralidhar k.s

Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva

Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.

Is This Answer Correct ?    23 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sreenu

Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.

So I(Current)= S (Apperent power)/Voltage only.

Is This Answer Correct ?    5 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / guru

i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....

Is This Answer Correct ?    3 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / murugesh.k

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    4 Yes 2 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sathishbabu t

p=v*i*cos

Is This Answer Correct ?    3 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / rahul

Full load current =Kva*1000 /v*Powe factor

Is This Answer Correct ?    0 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / kumar

formula of 3 phase power calculation

p=1.732*VL*IL*cos@

60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS

Is This Answer Correct ?    9 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

how can we calculate the ampacity of the electrical wire/cable. and what are the factors must be considered. pls. elaborate.

0 Answers   Webel,


Everybody Knows What is ACB, VCB but anybody tell me what is ST?

7 Answers  


power 148kw i need exat cable size in 148 kw in 3phase what size of cable can i used.

3 Answers  


When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.

3 Answers  


Do closed loops systems require manual input?

0 Answers   Ericsson,


How to know Resistance and Reactance value of main and aux winding of single phase capacitor start capacitor run induction motor to find capacitor value?

0 Answers   Siemens,


A 3ph load of 10 KW is equal to how many KW of single phase .

1 Answers  


CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS

0 Answers  


what is ICU and ICS in breaker ratings

1 Answers   QAFCO,


Can we use shunt trip coil instead of trip coil with protection relay for protection?

0 Answers  


IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?

0 Answers   ABB,


when the control mechanism is present for an ammeter(1-10A) and 1A current is apllied what will be the reading of the meter?

2 Answers   GATE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)