Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What will be the full load current of 60KVA UPS. Suggest
for this formula.

Answers were Sorted based on User's Feedback



What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sujit288

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    71 Yes 8 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / muralidhar k.s

Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva

Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.

Is This Answer Correct ?    23 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sreenu

Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.

So I(Current)= S (Apperent power)/Voltage only.

Is This Answer Correct ?    5 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / guru

i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....

Is This Answer Correct ?    3 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / murugesh.k

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    4 Yes 2 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sathishbabu t

p=v*i*cos

Is This Answer Correct ?    3 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / rahul

Full load current =Kva*1000 /v*Powe factor

Is This Answer Correct ?    0 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / kumar

formula of 3 phase power calculation

p=1.732*VL*IL*cos@

60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS

Is This Answer Correct ?    9 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

How we calculate the current carrying capacity of H.T. cabel?

0 Answers   Bhel,


working principle of generators?

4 Answers   Adani, MahaGenco,


Why we call cable rating in SQ.mm.If it is 240 SQ.mm how much the diameter possible?is there any calculation ?

4 Answers  


A resistance, inductance & capacitance are connected in series between points A & B.The voltage drops across the resistance,inductance&capacitance are found to be 40V,70V&100V respectively. What is the total voltage between between points A&B (Vab)? a)210V b)70V c)50V d)230V

6 Answers  


We have studied about many techniques for finding the stability of system, ROOT LOCUS, ROUTH, BODE PLOT, POLER PLOT etc. In these which is used where. what are the difference among them... PLZ tell me.......

0 Answers   MSEB,


What is mean by INRUSH CURRENT?

8 Answers  


Can an inverter be used as a converter? How?

0 Answers  


What is the difference between switch gear and control gear ?

2 Answers   QU,


Rccb trip or not with out neutral connect in three phase welding machine

1 Answers  


Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?

1 Answers  


In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3

1 Answers  


what is meant by generator differencial protection?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)