What will be the full load current of 60KVA UPS. Suggest
for this formula.
Answers were Sorted based on User's Feedback
Answer / sujit288
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
| Is This Answer Correct ? | 71 Yes | 8 No |
Answer / muralidhar k.s
Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva
Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / sreenu
Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.
So I(Current)= S (Apperent power)/Voltage only.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / guru
i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / murugesh.k
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kumar
formula of 3 phase power calculation
p=1.732*VL*IL*cos@
60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS
| Is This Answer Correct ? | 9 Yes | 11 No |
Draw a SLD of DG distribution up to main LT panel?
explain working of differential protection for a transformer?
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
if two bulb of 50w &30w apply in series having 230v the which bulb glow bright ,why
What happened when capacitor connect series in ac circuit?
state the working principle of incondenscent tube?
is EEE eligible for getting electrical supervisor certificate ? if yes then from which state i sud apply
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
calculation of lad carryinc capacity of 6mm2 cross section wire in 415 voltage circuit. What will be the amps.
How we can measure the thickness of bus bar for a given load ? any farmula Plz elaborate clearly.
pls someone send me sample question papers along with the key.thanks in advance
WHAT IS DOL STARTER? HOW IT WORK? GIVE ITS CONTROL AND POWER DIAGRAM .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)