Answer / divyaprabha
online ups is the one which in on position (both cases:
powersupply on&off).but in case of offline ups is on at the
time power failure.
| Is This Answer Correct ? | 430 Yes | 93 No |
Answer / ravi k lavu
On line UPS means Supply will come from batteries on line
and charging also on line.
In OFF line UPS supply will come from batteries when main
line supply fails.Batteries will charge on line.
| Is This Answer Correct ? | 350 Yes | 69 No |
Answer / ghanshyam pandey
In ONLINE UPS, the load is always connected to
inverter output only in both the cases, whether normal
power supply is available or not.
In OFFLINE UPS, Inverter output is connected to load only
when normal AC power supply fails, means when AC power is
available it is directly goes to output.
| Is This Answer Correct ? | 241 Yes | 26 No |
Answer / martin
Online UPS is the one which gives output all the time from
battery whether there is power failure or power on. You
get backing from battery all the time.
Offline UPS supplies Mains to the output when power supply
is regular and charges batteries as well at the same time.
When power fails it switches those batteries to produce
output for power backup.
| Is This Answer Correct ? | 157 Yes | 29 No |
Answer / muteka
Online UPS is the one which gives output all the time from
battery whether there is power failure or power on. You
get backing from battery all the time.
Offline UPS supplies Mains to the output when power supply
is regular and charges batteries as well at the same time.
When power fails it switches those batteries to produce
output for power backup.
| Is This Answer Correct ? | 105 Yes | 14 No |
Answer / ganesh.raj
A standby UPS or "offline UPS" draws current from the AC
outlet and switches to battery within a few milliseconds
after detecting a power failure.
The line interactive UPS "interacts" with the AC power line
to smooth out the waveforms and correct the rise and fall of
the voltage.
The "Online UPS" is the most advanced and most costly UPS.
The inverter is continuously providing clean power from the
battery, and the computer equipment is never receiving power
directly from the AC outlet. However, online units contain
cooling fans, which do make noise and may require some
location planning for the home user or small office.
| Is This Answer Correct ? | 96 Yes | 17 No |
Answer / gobhi
on line ups having dual conversion
off line ups having one conversion
| Is This Answer Correct ? | 90 Yes | 24 No |
Answer / john
Online UPS, it is getting power AC is converting to DC, then
the DC source stored to Battery at power supply on mode when
power fail, the DC sorce is changed to AC by inverter so
output power is having without noise.
OFFline UPS is having automatic voltage regulator, it
getting power from supply, it is regulated by AVR, then
power stored to battery so the change over time approx 2ms
to 5ms so change over noise comes.
| Is This Answer Correct ? | 81 Yes | 43 No |
Answer / hasan
Online UPS is unterrupted power suppy to the load,
Offline UPS can't ensure uninterrupted power supply, it
depends on the tolerance of the load. For any sophisticated
equipment (medical equipment), Online UPS is recommended.
| Is This Answer Correct ? | 59 Yes | 25 No |
Answer / saravanan
On line UPS means Supply will come from batteries on line
and charging also on line.
In OFF line UPS supply will come from batteries when main
line supply fails.Batteries will charge on line.
| Is This Answer Correct ? | 26 Yes | 4 No |
what is the difference b/w absolute encoder and incremental encoder?
Hi,I am working in abroad for more than 3 years in a company operating with 11kv and 6.4 MW power. I need c licence in India,can I? some other says only i can get if i work for 2 years in india only! anybody kindly clarify by doubt.Thanks
oltc of a transformer, how it works? and what are the equipment consist of describe briefly?
use of automatic voltage regulator & input voltage of it?
List examples of current sources?
we have 3 phase 4 wire supply 230/415 V.AC and our distribution is single phase or we have all single phase 220 v,ac operated appliances. and noted the current with help of clamp meter Red to N = 20 Amps. Yellow to N = 45Amps and Blue to N = 30 Amps ( total is 95 Amps ) what will be neutral current on the main .
how to select overload-relay for perticular motor 1.for D.O.L. starter 2. for Star-delta starter ????
HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION
what is vibration?
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.
what is meant by PU value ? anyone can you explain briefly to me ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)