In any relay Set earth fault to minimum That means If Earth
fault range is 20 to 80 % of secondary current then set it
to 20% . In case of over current calculate rated current
and add 5%for relay & ct error and 5% to over load that
means set it to 110% to full load capacity.
If for 200/1 CT If full load current is 160 that mens 80%
to secondary current of Ct+10% relay CT error and Over load
that means relay ia seted to 180A interms of secondary at
0.9 a that means 90%
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / vijay raskar
When earth fault is occured then relay is set at 2.5 times
than rated current.
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / erharisheee51
we have to connect earth fault relay through current
transformrs , at the neautral side of the generator and
transformers.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / j.kesavan
POWER CIRCUITE R,Y,B PHASE USING THREE CT ,THIS CT OUT PUT
CONNECT IN OVER CURRENT AND EARTH FAULT RELAY , IF ANY ONE
PHASE TAKE MORE CURRENT OR EARTH FAULT THIS RELAY WILL
TRIP.SETTING THIS RELAY MINIMUM CURRENT,MINIMUM DELAY.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / motilal sahu
WHEN EARTH FAULT OCCURE HIGH CURRENT FLOW THOUGH LINE.
IF THIS CURRENT IS 10-115 TIMES OF FULL LOAD CURRENT THEN
SHOW THAT EARTH FAULT OCCURE
SO SET THE RELAY FOR 10-15TIME OF FULL LOAD CURRENT
| Is This Answer Correct ? | 6 Yes | 10 No |
How cable from Kit-Kat to main switch, from starter to motor are designed?
how do we fix the rating of mcb required for a specific capacity of the electric motor
How to do fabrication , busbar and wiring cost for : 1. LT Panels 2. C& R Panel
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
What is the function of trip neutral close switch?
Why alternators are designed at 0.8 pf lag?
what is isolation Transformer?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
what is thermal setting and magnetical setting?
what is CRGO Transformers?
6 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd, TATA,
what are tpes of insulaors& its uses
WHAT IS BASICS TO SELECTION OF 11 kv Trasformer, send any calculation sheet for selection of transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)