how set earth fault over current in relay
Answers were Sorted based on User's Feedback
In any relay Set earth fault to minimum That means If Earth
fault range is 20 to 80 % of secondary current then set it
to 20% . In case of over current calculate rated current
and add 5%for relay & ct error and 5% to over load that
means set it to 110% to full load capacity.
If for 200/1 CT If full load current is 160 that mens 80%
to secondary current of Ct+10% relay CT error and Over load
that means relay ia seted to 180A interms of secondary at
0.9 a that means 90%
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / vijay raskar
When earth fault is occured then relay is set at 2.5 times
than rated current.
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / erharisheee51
we have to connect earth fault relay through current
transformrs , at the neautral side of the generator and
transformers.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / j.kesavan
POWER CIRCUITE R,Y,B PHASE USING THREE CT ,THIS CT OUT PUT
CONNECT IN OVER CURRENT AND EARTH FAULT RELAY , IF ANY ONE
PHASE TAKE MORE CURRENT OR EARTH FAULT THIS RELAY WILL
TRIP.SETTING THIS RELAY MINIMUM CURRENT,MINIMUM DELAY.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / motilal sahu
WHEN EARTH FAULT OCCURE HIGH CURRENT FLOW THOUGH LINE.
IF THIS CURRENT IS 10-115 TIMES OF FULL LOAD CURRENT THEN
SHOW THAT EARTH FAULT OCCURE
SO SET THE RELAY FOR 10-15TIME OF FULL LOAD CURRENT
| Is This Answer Correct ? | 6 Yes | 10 No |
We all have seen transmission and Distribution lines In transmission lines the voltage is high and current is low(to reduce I^2r loss) and in distribution lines voltage is low but current is high however the size of transmission wires is bigger than that of distribution wires even though the amount of current carried by the distribution lines is more than that of transmission lines why?
why starting current is high and resistance is almost 0 during the starting of motor dc motor...?
What is super thermal power plant? and how it will differ from normal thermal power plant
what is auto re-closer?
what is the ambient temperature of transformer oil & winding?
25 kvar capacitor , how much current ? For 25 KVAR--Capacitor I = ?
-----------means a source which can supply a constant voltage to aload irrespective of the valu of load resistance.
Where is the best place to mount distribution panel in a house.
0 Answers Wantro Technical Services,
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
Why the power factor improvement is so important in industrial loads
ward lconard control
How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)