In any relay Set earth fault to minimum That means If Earth
fault range is 20 to 80 % of secondary current then set it
to 20% . In case of over current calculate rated current
and add 5%for relay & ct error and 5% to over load that
means set it to 110% to full load capacity.
If for 200/1 CT If full load current is 160 that mens 80%
to secondary current of Ct+10% relay CT error and Over load
that means relay ia seted to 180A interms of secondary at
0.9 a that means 90%
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / vijay raskar
When earth fault is occured then relay is set at 2.5 times
than rated current.
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / erharisheee51
we have to connect earth fault relay through current
transformrs , at the neautral side of the generator and
transformers.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / j.kesavan
POWER CIRCUITE R,Y,B PHASE USING THREE CT ,THIS CT OUT PUT
CONNECT IN OVER CURRENT AND EARTH FAULT RELAY , IF ANY ONE
PHASE TAKE MORE CURRENT OR EARTH FAULT THIS RELAY WILL
TRIP.SETTING THIS RELAY MINIMUM CURRENT,MINIMUM DELAY.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / motilal sahu
WHEN EARTH FAULT OCCURE HIGH CURRENT FLOW THOUGH LINE.
IF THIS CURRENT IS 10-115 TIMES OF FULL LOAD CURRENT THEN
SHOW THAT EARTH FAULT OCCURE
SO SET THE RELAY FOR 10-15TIME OF FULL LOAD CURRENT
| Is This Answer Correct ? | 6 Yes | 10 No |
What is the limitation of kirchoffs law?
What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer
we all know that in capacitor there will be no ay physical connection between the two electrodes of the capacitor ,and the charge is stored between these electrodes during charging , so with out any physical connection how these charge is transferred from one plate to the another plate during the discharge?????
what is motor contrl center .
Explain what are inter-poles and why they are required in a dc machine.
In Power transformer oil temperature or winding temperature will be high
HOW WOULD YOU PRESENT THE POWER FACTOR PRACTICALLY ON A GRAPH
if a number of plc s are there then how many modbus to be used
i am trying to PSUs/govermeant jobs since last 2 years but still i m not success, plz help me.
what is advantage of using star to delta in place of dol starter
please mention the minimum IR value for different voltage systems
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)