What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
Answers were Sorted based on User's Feedback
Fourmela No 1 power in one phase/Voltage in one phase(I.e phase voltage)
example there is a 300 KVA 11KV/433 V transfomula. Power in one phase 300KVA/3 =100KVA both in HT & LT side, Phase voltase in HT side 11/√3 = 6351Volt .Phase voltage in LT side 433/√3 = 250 Volt.
According to formula HT side current 100,000/6351 = 15. 7 amps. and LT side current 100,000/250 = 400 amps
Formula No 2 for HT side transformer in kVA/20 and for LT side KVA×4/3. field lineman are using this formula.
According to this formula 300 KVA transformer's HT side current 300/20 =15 amps apporximately +5℅ may added for big size to accurate value. And LT side current 300×4/3 = 400 amps apprx.
In general formula for 300 KVA 11KV/433V transformer HT side current KVA/LV×√3 i.e 300000/11000×1.732 = 15.7 amps .LT side current 300000/433×√3 = 400 amps
PRADYUMNA CHANDRA PANDA
mob No 943
7917849
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / haider
P=Root3 *VIcos$
P=KVA rating of DTR
V=primary volage (HV side)
cos$=power factor
Exp:
100KVA DTR
primary volage =11000V
let Power factor=0.97
I=kva/1.732*11000*0.97
I=5A
| Is This Answer Correct ? | 12 Yes | 18 No |
What is class ab operation?
why stator winding of synchronous machine are connected in star connection ?
State The Difference Between Generator And Alternator?
Actuality I have at home electrical panel with 220v 50hz, and I want to converter from there to 110v 60hz, to wiring on the half of my house. Also I like to keep another half of my house with the original 220v 50hz. What is the best and safety way to do?
why power is generatd at 50 hz only..? can we do this on another freq...?
Define delay time.
when we megger is not damaged when we are measuring very low resistance? high d.c. voltage is produced in megger so according to i=V/R. current will be high so what is the reason ?
What are test values for an 63 KVA and 100 Kva Distribution Transformers for the following typical tests 1)Magnetic balance 2)Short circuit test 3)Open Circuit test 4)Vector group confirmation test .please give me the standard values for all the above tests.
What can you contribute to the progress of our Company as an employee if you are selected?
Suppose i Have an Ac motor of 25Hp 1500 Rpm 50 Hz Can i run a motor 2500 Rpm by AC drives by increasing a frequency either it safe or not ....
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
What is Negative Potential Bias
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)