What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
Answers were Sorted based on User's Feedback
Fourmela No 1 power in one phase/Voltage in one phase(I.e phase voltage)
example there is a 300 KVA 11KV/433 V transfomula. Power in one phase 300KVA/3 =100KVA both in HT & LT side, Phase voltase in HT side 11/√3 = 6351Volt .Phase voltage in LT side 433/√3 = 250 Volt.
According to formula HT side current 100,000/6351 = 15. 7 amps. and LT side current 100,000/250 = 400 amps
Formula No 2 for HT side transformer in kVA/20 and for LT side KVA×4/3. field lineman are using this formula.
According to this formula 300 KVA transformer's HT side current 300/20 =15 amps apporximately +5℅ may added for big size to accurate value. And LT side current 300×4/3 = 400 amps apprx.
In general formula for 300 KVA 11KV/433V transformer HT side current KVA/LV×√3 i.e 300000/11000×1.732 = 15.7 amps .LT side current 300000/433×√3 = 400 amps
PRADYUMNA CHANDRA PANDA
mob No 943
7917849
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / haider
P=Root3 *VIcos$
P=KVA rating of DTR
V=primary volage (HV side)
cos$=power factor
Exp:
100KVA DTR
primary volage =11000V
let Power factor=0.97
I=kva/1.732*11000*0.97
I=5A
| Is This Answer Correct ? | 12 Yes | 18 No |
which turbine has high thermal efficiency a)open gas turbine b)close gas turbine
What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing?
what is difference between DC and Ac
What are the tests carried out on transformer while testing at sites?..Pls explain me in detail
what is S.D.F stands for ? (S.D.F unit 80 amp , TPN )
what is effect of length of air gap on performance of dc motor and generator?
what is the function of conservater in transformer
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
STATE AND EXPLAIN SUPER POSITION THEOREM.
what is meant by tranformer impedance?
why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
What is the principle of HIGH SPEED DIRECT DRIVE MOTOR ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)