what is the function of conservater in transformer
Answers were Sorted based on User's Feedback
Answer / anil bhatia
1)The conservator is a small tank which is connected to
main tank /transformer through a pipe containing buchholz
relay.the outside vent of conservator is connected through
silica gel.
During high load heat generated in winding and absorbed by
tranformer oil.the oil expands and passes throuh buchholz
relay to conservating tank to store it.the air expilit out
throuh outsite vent.
2)During low load this oil contrast and go down to main
tank . during this process silica gel absorb moister from
the air so this moister donot mix with oil and keepit dry.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / sajid
for the storage of excessive transformer oil during heating
and expansion and also buchholz relay is installed at a
certain level to avoid any damage.
Is This Answer Correct ? | 3 Yes | 1 No |
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
What range of speed can you get with the armature control method of speed control of d.c. Shunt motor?
How to find the maximum load(in KW)in a big industry, having motors,lights,lifts etc..?
While testing the value of the resistance for the earthing rod, two auxillary rods are connected to the earthing tester.What is the working function of a earth tester?
what is the different types of cable lugs?
2 Answers Green Power, Kum Yang,
hi sir i have load of 17.5kw in 3 phase lighting circuit which mcb i can use
how many types of accuracy class in ct? what is meaning of 5p20?
I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel of 400 kVAR(LT).Now if i want to remove the LT APFC panel and install a HT(11kV) APFC panel on the HT side is the HT APFC panel will work same as the LT APFC panel(improve the power factor),if yes what will be rating of the HT APFC panel?what is the formula to calculate HT APFC panel rating???
What is the minimum setting in REF relay because i am facing some problem whenever power resumes after power failure my transformer is tripping because of REF trip. I am using CSPC make numerical relay(DIP switches). Now setting is 15 percentage. What is the reason for this triping. I sm waiting for answer
What is the transfer function?
Describe how a salient pole / projecting pole rotor differs from a cylindrical rotor and state the application of each rotor respectively
The inventer is a battery, but if lost current at home u will turn on the fan but the is AC and inventer battery is dc . Then how the fan was rotating. What device Or machine in fan converst the Dc power to Ac power