What is the purpose of taking Capacitance and Tan Delta
Test in Transformer bushing?
Answers were Sorted based on User's Feedback
tan delta (loss angle ) and cap is taken of the enquipment
such as CTs and TRF bushings wherein paper and other
material is utilised in its insulation.
tan delta and cap values indicates to you the condition of
the bushing insulation.
if a plot is plotted aginst the no of years of the bushing
in service and the value of tan delta taken every year, you
shall get the trend of insulation detoriation.
the higher side of tan delta value is 0.007.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / greg
tan delta gives the ratio of resistive current to capacitive
current.therefore it shows the amount of resistive current
flowing through the insulation,in other words it denoted the
dielectric strength of bushing.
Is This Answer Correct ? | 0 Yes | 0 No |
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
What are the point of a single core cable to be earthed?
why is using sensor?what is differece between photoelectric and proxmitty?
why plc need seprate earthing?
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
0 Answers ABC, Reliance Life Sciences, TCS,
What power factor maintain you maintain at u r organisation
what will happen if one of the phases from a 3-phase motor is disconnected?? stop/run at 2/3rd speed or run at same speed????
Merz-Price circulating current principles is more suitable for
what is the use of excitation transformer in LAVT PANEL?
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
Why the transformer rating is denoted in VA rating why not in KW
What is the accepted limit to increase the choosen transformer capacity over the load and why ?