if suppose boiler has high heavy tube leakage, so in which time we feed the water in a boiler. can we stop the feed water at particular combustion temperature.
Answers were Sorted based on User's Feedback
Answer / mayur mukaty
In normal operation if boiler feed pump stop within a 1 min level goes down to become zero. For best practices when tube leakage heavily fuel feeding stop, take down the load, maintain draft , and take manually FRS system to maintain drum level as for as possible. For latest technology improvement ultra sonic senser are deployed for detection of location of tube failure.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / alok bhattacharya
When boiler is steaming, only then leak will develop because of steam pressure and faulty tube part. Now in case of heavy tube leakage, boiler must be stopped immediately and maintain drum level in order to avoid starvation and further damage of tubes. Moreover boiler need to be depressurized simultaneously.
Thanks
| Is This Answer Correct ? | 0 Yes | 0 No |
Hi,
I am assuming you want to stop the feed water to attend the tube leakage. But it is not clear what the question is about. IF the light up has been done,I do not think the flow of the water in boiler can b stopped. Secondly if light up has not been done then better to shut down the unit and properly take up tube leakage attending procedure.
| Is This Answer Correct ? | 0 Yes | 1 No |
why not maintain Ph 7.0 in Boiler because 7 Ph is not acidic and not basic.
We know primary ,secondary air so, What is the work of Tertiary air in Thermal power plant
if suppose boiler has high heavy tube leakage, so in which time we feed the water in a boiler. can we stop the feed water at particular combustion temperature.
what is voltage transformer explain in details
5 Answers Khulna Power, NCC, Reliance Power,
what is actual CAL MODE & cal means?
what is need of primary water system in power plant?
how shall you calculate PLF on the basis of percentage auxillary load factor
What do mean by 3t
1 Answers Aman, Birla, Grasim,
What happen when the AVR of the generator fails? Will it cause power instability and total failure of the alternator?
difference between vaccum pump and ejector
2 Answers NTPC, Tata Steel Limited,
operation
What is the use of Hydraulic Coupling in-between BFP pump & BFP Motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)