if suppose boiler has high heavy tube leakage, so in which time we feed the water in a boiler. can we stop the feed water at particular combustion temperature.
Answers were Sorted based on User's Feedback
Answer / mayur mukaty
In normal operation if boiler feed pump stop within a 1 min level goes down to become zero. For best practices when tube leakage heavily fuel feeding stop, take down the load, maintain draft , and take manually FRS system to maintain drum level as for as possible. For latest technology improvement ultra sonic senser are deployed for detection of location of tube failure.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / alok bhattacharya
When boiler is steaming, only then leak will develop because of steam pressure and faulty tube part. Now in case of heavy tube leakage, boiler must be stopped immediately and maintain drum level in order to avoid starvation and further damage of tubes. Moreover boiler need to be depressurized simultaneously.
Thanks
| Is This Answer Correct ? | 0 Yes | 0 No |
Hi,
I am assuming you want to stop the feed water to attend the tube leakage. But it is not clear what the question is about. IF the light up has been done,I do not think the flow of the water in boiler can b stopped. Secondly if light up has not been done then better to shut down the unit and properly take up tube leakage attending procedure.
| Is This Answer Correct ? | 0 Yes | 1 No |
What is indipendant power plant
Our 8mw steam turbine (condensing cum extraction) exhaust steam temperature is high even after taken it in hogger why
1 Answers Bombay Rayon Fashions,
Why reheater is not used after IP turbine.
How to decide Heating surface area of boiler on their steam generating capacity?
What is A.T.T.?
Calculating Seawater consumption for SWFGD system
What is the the sequence/logic of burner management system in boilers. What is purging and scavenging?
What is droop.
2 Answers Dhampur Sugar Mills, Elaf,
how shall you calculate PLF on the basis of percentage auxillary load factor
What is reheater protection based on what mft will be act on RH protection
how mony power plants in India
what is block out in thermal power plant?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)