why the output sugnal is 4-20 ma and not 4-25 ma?
Answers were Sorted based on User's Feedback
Historically, the 4-20 mA electronic control signal replaced the 3-15 psi, 20-100 kPa or 0.2-1.0 bar pneumatic control signals and its competitor 10-50 mA.
The ratio of contorl signal span to its 'live zero' is the same in all cases: 4:1
The ratio of span to the 'live zero' for 3-15 psi is:
span = 12 psi (15-3)
live zero = 3
ratio span:live zero = 12:3 = 4:1
The ratio of span to the 'live zero' for 20-100 kPa is:
span = 80 psi (100-20)
live zero = 20
ratio span:live zero = 80:20 = 4:1
The ratio of span to the 'live zero' for 0.2-1.0 bar is:
span = 0.8 bar (1.0-0.2)
live zero = 0.2
ratio span:live zero = 0.8:0.2 = 4:1
The ratio of span to the 'live zero' for 10-50 mA is:
span = 40 mA (50-10)
live zero = 10 mA
ratio span:live zero = 40:10 = 4:1
The ratio of the span of the active control signal to its live zero is identical in all cases.
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / satish singh
because in this range the current value is continuity /or we can say that in thios range the value is linear
| Is This Answer Correct ? | 4 Yes | 2 No |
if zero signal is send in process then there can be cable cut then not recognize that this is signal transmit or cutting signal
| Is This Answer Correct ? | 2 Yes | 0 No |
Why we use 4-20mA signal?? Not start from 0-03mA? & 20mA??
· We can not use 0-20 mA signal cos then it becomes very difficult to distinguish between "zero" signal and "instrument fail" signal.
· Where as if we use 4-20 mA. its very easy like when we get 4mA means the signal is at low level and if it is below 4mA it shows us that the instrument is not working or it is failed
•That may have been one of those arbitrary decisions that is sometimes made when a standard is developed. In addition to providing a non-zero minimum to allow detecting signal loss, the minimum signal voltage provides for a margin between the minimum signal and any noise that might be present. Perhaps someone determined that 4ma was large enough to help with noise and thought that the numbers worked out conveniently. A 16 volt difference between min and max, difference = 4 X min, range of 20% to 100%, perhaps seemed easier to work with than 17 volts, 5.67 X min and 15% to 100% or 18V, 9 X & 10% to 100%
•This 20 mA signal is not enough to trigger a spark and therefore we can limit fire hazards in plant area
•As there is a leakage current so 0 to 3 MA, so we consider as 4-20MA. But in some cases we will find some transmitters 0-20MA which are more costly than 4-20mA
| Is This Answer Correct ? | 1 Yes | 0 No |
@Marmkijani
The main reason for 4-20mA is that 2-wire field instruments need to use 3.5mA to power their own electronics in order to make a measurement and to control the regulated output.
4-20mA is also, as you pointed out, a range in which the energy in the circuit is low enough to qualify for Intrinsic Safety approval (when used installed properly with an approved DC power supply and I/S barrier).
The "live zero" is nice and convenient as a diagnostic for an open circuit fault, but it was not the main reason for 4-20mA; powering field instruments was the main reason.
| Is This Answer Correct ? | 0 Yes | 0 No |
Describe all types and levels (4-20mA, 0-10V, mV, pulse, etc.)of analog and digital I/O used in process control application.
what u mean by speed control in turbin? how it was working?
how to measure oxygen which methods are using?
all types instrumentation questions want
0 Answers Bhel, Descon, HBL Power Systems,
what is pyrometer? which purpose it has to be used?
what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.
While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Transmitter or at ISB.Why not Shield Terminal connected at both ends.If the Reason is to avoid Noise interference,which type of noice that is interfering.Is the Noice from the 24 VDC supply terminals or from any external source.
how to define range of dp level xmeter in open tank
the whole paper was based on Transducers..questions like define repeatability, error,accuracy,precision..den there were many q. on the conversion of Pa to mmHg and other units.. also..der wer few Q. on some level sensors(with diagram)
Linear amplifier.
can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.
plz exlain the dcs system of ABB sympony hamnony
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)