transmitter in 3 connection +,-,And test mode so how Use To Test Mode
The 'test' connections on a 2 wire, loop powered pressure transmitter have a diode behind them.
If a milliampmeter is connected across the test terminals (in parallel with the diode), the impedance of the meter is less than the diode's, so current will flow through the milliampmeter. There is not enough voltage drop to forward bias the diode and the diode will not conduct with a low impedance meter circuit connected across it. The diode turns off and the current flows through the meter.
Test terminals are provided for loop troubleshooting so that loop current can be measured without breaking or opening the loop circuit so that the milliampmeter can be put in series in the loop circuit.
Carl Ellis
Measure First
| Is This Answer Correct ? | 13 Yes | 0 No |
What should be the stanchan Height for installation of Smoke detector & toxic gas detector in field,according to qatar standard
when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICATOR.
What is the difference between intrinsic instruments and ATEX instruments?
how to know the URL and LRL for steam drum level and why the calibration range is in negative ?
what is use of communication wire in multipare cable(oil and gas field), why this communication wire not used in single pair cable?
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
Troubleshoot to the device level basic process control systems given the Process and Instrumentation Diagram?
We are using Rosemount 5400 series Radar Level Transmitters in all types of Sump Applications having oily water hdrocarbon petrochemical nature. What we are facing the problem frequently is that always getting reading frezzed at some value. If we do power recycling , sometimes it is working . then making same freezing problem. If anybody faced before such type of problem and also having solution , Please give the answer.
steam drum level transmitter calibration procedure? with example?
Could anybody tell how much amps will a single input to plc will consume?
How to convert m3/hr in tonnes/hr
What are the logic behind 2x2 and 2x3 logic and more when ask in interviews
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)