Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is Automatic Voltage regulator(AVR)?

Answers were Sorted based on User's Feedback



What is Automatic Voltage regulator(AVR)?..

Answer / boopathiraja

AVR is an abbreviation for Automatic Voltage Regulator.It is
important part in Synchronous Generators, it controls the
output voltage of the generator by controlling its
excitation current. Thus it can control the output Reactive
Power of the Generator.

Is This Answer Correct ?    47 Yes 2 No

What is Automatic Voltage regulator(AVR)?..

Answer / srij21

AVR's are normally used in the Diesel Generators.They are
used to control the output voltage depending upon load
connected , such that, the load will not cause any voltage
fluctuation and damage to the DG.

Is This Answer Correct ?    33 Yes 14 No

What is Automatic Voltage regulator(AVR)?..

Answer / pankaj

AVR generally used in generators The function of AVR is :
due to residual flux, initialy residual voltage build up in
the alternator, this voltage given to avr which compare the
output voltage of the alternator with the setr efrance
voltage and controls the output voltage.

Is This Answer Correct ?    14 Yes 1 No

What is Automatic Voltage regulator(AVR)?..

Answer / ash

The AC synchronous generator usually uses the AVR to
regulate the magnetic field/s strength of the exciter
stator. The AVR samples the main generator/s Real-time
output voltage ,which compared with the value preset, then
there will be a result ,which can regulate the PWM(pulse
width modulation).
If the output voltage value is higher, then the narrow
pulse width will be output, and vice versa, then using
these pulse to control the high-power transistor to control
the current time, which pass the exciter stator winding.
Thus the magnetic field strength will be change in the
opposite of the main generator output voltage. Namely, the
higher voltage output, the lower exciter stator magnetic
field, and vice versa, so as to achieve the purpose of the
negative feedback regulation.

Is This Answer Correct ?    7 Yes 0 No

What is Automatic Voltage regulator(AVR)?..

Answer / bhanu pratap

to understand the function of AVR first v have to understand
concept of reactive power....

all of u know reactive power..



a generator has active power and reactive power... infact
with out reactive power ther will be no generation..


reactive power is the one which is the power consumed for
the establishment of magnetic flux in the machine without
which no generation takes place....

coming to the AVR..
consider a generator supplying to the grid.. as the grid is
not purely resistive.. it generally is inductive since loads
connected to grid(consider industries)are inductive..
generator tries to draw reactive power from the grid for the
development of its magnetic flux...(under constant frequncy)




when frequncy changes ..it disturbs the magnetic flux ...so
the geneartor tries to draw more n more reactive power from
the grid.. if this happens .. rotor of the generator will
get heated due to this reactive power..


so here comes d AVR... avr produces the xtra amount of
voltage required for the machine to maintain its magnetic
fld so that (V/F) will be constant...


thats wat i feel.. inform if any corrections




when

Is This Answer Correct ?    9 Yes 3 No

What is Automatic Voltage regulator(AVR)?..

Answer / atreya

AVR stands for Automatic Voltage Regulator. In case of
synchronous generators, it is used to control the generator
terminal voltage and maintain it at a certain set-point(
say 11 kv) by controlling the excitation voltage of the
exciter of the sync. generator.

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How to check the specific gravity of the two 12 V batteries connected in series to a 24 V UPS and inverter ? will we have to disconnect all the connections and turn off the UPS and inverter or not ? will we have to check specific gravities in each cell of the two batteries ? what is the name of the instrument that is used to check the specific gravity and whats the procedure to check the specific gravity with it ? thanks

2 Answers  


How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.

0 Answers  


what is the id1 & id2 setting in differential protection relay of CSPC?

0 Answers   Wartsila,


WHAT WILL HAPPEN IF INPUT SUPPLY OF RCBO IS CONNECTED TO OUTPUT SIDE

2 Answers   ABG Shipyard,


why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?

0 Answers  


which plant has high load factor

10 Answers   APTransco,


What is Load commutation and how it is done?Cite some example where this type of commutation is used

2 Answers   NTPC,


A 6-pole, 50 Hz, 3-phase synchronous motor and on 8-pole, 50 Hz, 3-phase slip-ring induction motor are mechanically coupled and operate on the same 3-phase, 50 Hz supply. If they are left open-circuited, then the frequency of the voltage produced across any two slip rings would be

2 Answers   L&T,


if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.

0 Answers   Power Plant,


if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?

1 Answers  


When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.

3 Answers  


what is relay what is protection & contact multiplying relays where it is used function in brief

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)