i want the equation of this question.
Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer: 239.2 mmH2O
Present max flow rate = 1700 nm3/hr
Present max DP (at max flow rate) = 120 mm H2O
New max flow rate = 2400 nm3/hr
New max DP (at new max flow rate) = x
2400/1700 = 1.412 or an increase of 141.2% in flow rate.
The DP and the flow rate relationship is a square root relationship, but the calculation is based on normalized percentage.
X = 1.412^2*120
X = 1.993*120
X = 239.2 mmH2O
The increase in max DP from 120 to 239.2 mmH2O is an increase of
239.2/120 = 1.993 or 199.3% increase in max DP at max flow rate.
Sq root of 1.993 = 1.412 or 141.2% increase in max flow rate (2400/1700)
Carl Ellis
Measure First
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / alim
I think the equation is not straight forward, you need some repetition formula for calculating this.
Normally, I will use some software to do this kind of calculation such as InstruCalc. The data that you presented in the question is not enough. I am assuming that you are using the orifice in as the flow element, then you still need viscosity and specific gravity of the fluid.
Is This Answer Correct ? | 1 Yes | 1 No |
what is diffrence between analog card and digital card in plc.how analog card work,Please explain in detail.Please send it on abhi_vyas@sify.com
Good Evening all.My question is - For a feed water line to an equipment if i need to measure the flow we will use orifice /magnetic/vortex depend on cost/spec.If i need to measure a ''Alarm''signal and ''Interlock'' from one point i think we can use orifice type in one location with 2 different tapping points - one for alarm and one for an interlock to flow valve..If in case i need to have both these signals(Alarm & interlock) from magnetic flow meter,is it possible??will 2 seperate sensors will be located inbuilt r we can program it ??..i thk we can have one transmitter with these 2 signals...need to know any technical issues are there?pls clarify
What is meant by calibration
what is Instrument Schedule, and what it is mainly used for?
WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??
2 Answers TATA, Tata Steel Limited,
what type of cables are used for f&G systems and detectors, what is the standard colour?
[ MITUTOYO / TESA / KUMAUN / MAHR / BRITOOL / TOHNICHY / DIATEST-GERMANY / IMADA / TECKLOK / SYLVAC /ADITYA=ACCURATE / BAKER/ CRYSTAL / FLUKE-RAYTEK ETC. 5.=SUPPLY= VERNIER CALIPERS / MICROMETERS / HEIGHTGAUGES / SLIPGAGE / BORE DIAL GAUGES / MEASURING PINS / TORQUE WRENCHES / GAUGES.. PLUGGAUGES / RINGGAUGES / SHORE A / D HARDNESS TESTERS / DIAL THICKNESS GAUGE / FEELER GAUGES / ELECTRONIC COMPARATORS WITH PROBES / DFTMETERS / SURFACE ROUGHNESS TESTERS / DIGITAL= COATING THICKNESS METERS / PROFILE PROJECTORS /.. WE ARE ALSO DEAL IN == DIGITAL TACHOMETERS / =MULTIMETERS! / VIBRATION METERS / MEGERS- INSULATION METERS / =TE! MPRATURE INDICATORS / SOUND-LEVEL METERS / ETC... =AGENCY- FLUKE- RAYTEK.. MECO....LUTRON...KYORITSU....RION
What for barriers are used in DCS & PLC systems?
If I want to buy a pressure switch & 3-way valve for hot water application then witch parameter I should consider.
what is lead lag compensator and for wat v using that???
How to interfacing microcontroller with a DC motor
Where is the flow transmitter installed with respect to control valve, state reason.