i want the equation of this question.
Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer: 239.2 mmH2O
Present max flow rate = 1700 nm3/hr
Present max DP (at max flow rate) = 120 mm H2O
New max flow rate = 2400 nm3/hr
New max DP (at new max flow rate) = x
2400/1700 = 1.412 or an increase of 141.2% in flow rate.
The DP and the flow rate relationship is a square root relationship, but the calculation is based on normalized percentage.
X = 1.412^2*120
X = 1.993*120
X = 239.2 mmH2O
The increase in max DP from 120 to 239.2 mmH2O is an increase of
239.2/120 = 1.993 or 199.3% increase in max DP at max flow rate.
Sq root of 1.993 = 1.412 or 141.2% increase in max flow rate (2400/1700)
Carl Ellis
Measure First
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / alim
I think the equation is not straight forward, you need some repetition formula for calculating this.
Normally, I will use some software to do this kind of calculation such as InstruCalc. The data that you presented in the question is not enough. I am assuming that you are using the orifice in as the flow element, then you still need viscosity and specific gravity of the fluid.
| Is This Answer Correct ? | 1 Yes | 1 No |
please help me to get the below mentioned quires,which i have to submit for my client.[INSPECTION TEST PLAN] 1]I.T.P for Calibration of all instrument. 2]I.T.P for SS tubing. 3]I.T.P for Fire & Gas devices. 4]I.T.P for CCTV & telecommunication. 5] I.T.P for loop checking.
What is possitive and negative feedback?
In control valves (like feed water control valve) we will give 3 kg pressure and how it controls 110 kg of water pressure?
hi vishok this is noor plz tell me what type problems will occured i use T/C in the place of RTD in (FEED WATER TANK),plz send ur e-mail address to my ID (mail2noor.hyd@gmail.com)
What are use of positioner.
What is rtd output signal
how will you segregate the alarm levels in alarm management system during factory Acceptance Test
What is the difference between relative vibration
How ejector(or)evactor air pump is working in thermal power plant?
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
which transister (npn or pnp) is used in vibration monitoring for negative voltage?
hye SAM acn u send your e mail id, so that i can solve my query through e mail?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)