Answer / priyabeet das
1st of all this is a live zero concept. now what is live zero? suppose the range is 0-20ma.so the Tx will indicate0ma as lower value.but when there is no i/p or there is some fault in process then also Tx will show 0ma as reading. so , seeing 0ma we cant decide whether it is for any i/p or not. that is why the lower LRV is chosen as 4ma.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / suresh
This is Live zero concept. In case of airsupply failure or
Current loop failure the Control equipment (DCS/PLC) senses
below 3.5mA, considered as Loop Open circuit.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / sudipta,iter
bcz 4 ma is the amount of current that occurs when there is
no input to the transmistter and coresponding pressure is
3psi.this is called as live zero concept.so by using thus
we can detect error easily .thats why we usese this value.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / oza paritosh m.
It is also useful for instrumentation guy to differentiate
between process zero and instrument zero.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / abu maryam
For 4 mA & 3 Psi it is virtual zero to differ with actual zero (0 mA & 0 psi) to define if actual signal (mA & air )is found or not.
For 4: 20 mA
In my opinion the reason for use these values is most electronic cards work from 1: 5 volt and resistance (hart ) is 250 ohm
then V=I * R
R= 250 ohm and V= 1 volt so I= 1/250=,004 A= 4 mA
R= 250 ohm and V= 5 volt so I= 4/250=,02 A= 20 mA
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dr
Why not more than 20ma??
More than 20ma continuously for 20Sec will make your heart
to malfunction.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / prashant jadhav
If we look at Hazardous and power consumption point, 4-20 mA is the perfect range qualifying both points...Not able to produce large sparks and consumes least power...So it is made as a Standard signal..
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rajesh j
4-20mA is because the least power consumption range with
linearity and to detect even when signal line opens
3-15psi is because of the minimum linear range for which
the control valve will respond to pneumatic signal
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / rafiq
these are standared things. its nothing but a i to p
converter. for 4 ma it will convert 3 psi and for 20 ma it
has 15 psi.
| Is This Answer Correct ? | 2 Yes | 8 No |
what is vibration sensor working principal and how many types its has??
Identification of control valve parts.
0 Answers CCIE, Oil and Gas Jobs,
where is a level displacer is used?
how to calculate range of level transmitter?
What is the procedure of calibration of Load cell?
how to adjust relay in smart positioner ?
What is the role of Integral in pid control?
If you calibrate a pneumatic pressure transmitter, how many adjustments are normally necessary or mandatory?
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
components of control circuit belongs to control valve
what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liquid density .73, transmiter fixed on a fractionation colum, under vaccume 10mbar
What is glanding
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)