there is one orifice plate already installed on 3" line, but
my previous engineer(who is not working here) removed that
tx, but now i want to take it in to the process, so now what
i have to do now? flow fluid is hytherm oil of temp. 260deg
& pressure is 3bar.
Answers were Sorted based on User's Feedback
In any industrial plant there will always be good records
and documentation on all equipment as well as all
instrumentation installed on the plant. The easiest in your
case is to find the FT tag number on the P&ID drawings or
the CCR faceplate and look at the data sheet of the missing
transmitter. The original calibration in differential
pressure will be on there as well as the model number of the
transmitter you need.
All you then have to do is calibrate the new DPT with the
diff press as per the data sheet and it will work as before.
In most cases the squire root extraction is done in the DCS
and not in the transmitter so try it just like this first.
The faceplate in the CCR will normally be set up to display
the min and max flow so that will not help you to find the
calibration diff pressure of the transmitter.
You can also try and find the original transmitter that was
removed and put power on it ans see what it was calibrated
for before. Even if the transmitter is faulty it might still
be able to display information. The is just as a last resort
since you cannot be sure if this calibration is what it
should be and it is better to double check it with the
documentation. This is just a method to double check
information.
As a desperate measure you can also measure the upstream and
downstream pressure as it is now during normal operation and
calibrate your transmitter to 1,5 that differential pressure.
For example:
Say your upstream pressure before the orifice is 300Kpa and
downstream it is 270Kpa you therefore have a DP over the
orifice of 30Kpa during normal operation.
Calibrate the transmitter for 0 to 45Kpa.
The flow indication inside the CCR will indicate the correct
flow since the extraction and the display is already setup
as it was originally. Have a look at what the % the flow is
indicated on the CCR faceplate. Since it is normal
operations it should be about 50% of the scale on the
faceplate. If it is not, modify the DPT calibration until
the current flow display about 50% of the full scale in the
CCR. You should be pretty close then.
This is not a very good or accurate way to do it and you
should keep on looking for the original design specs and
then re-calibrate the DPT when you found it.
Good luck
| Is This Answer Correct ? | 5 Yes | 0 No |
Dear Nitin,
Ideally you shall have all the records, but in case if you do not have the records then try to recalculate the DP value using orifice sizing. You can get data for process condition from your process engineer and B (beta value / bore i.d. from orifice plate itself).
If you do not know how to calculate DP the please forward all the process condition with Line size, Line schedule and B beta value to anadkat.jigar@gmail.com. I can recalculate it for you.
Hope this will help you out.
Best Regards,
Jigar Anadkat
anadkat.jigar@gmail.com
| Is This Answer Correct ? | 1 Yes | 0 No |
what is see back effect?
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..
List three types Level Transmitters with their working principles
1 Answers ABB, Bapco Bahrain Petroleum Company,
i have been asked by QAFCO to appear for interview for thy post of Instrument Designer(INTOOLS)..i m engineering graduate with 5 years exp. in design engineering.Will this job profile suit me??i need all ur help n suggestions for thy same?
1. what is modbus cable? 2. what kind of communication we are using for the interface of DCS, ESD and Third party cabinets? 3. What is serial communication and peer to peer communication?
Is it ok, to use non-contact type Radar type LT, on a tank that is half circular from the bottom side? If yes the, isn't the waves gonna bent in other directions?
0 Answers Process Control Technologies,
why level transmitter input is given 4to20ma
How digital input and digital output 's are working in dcs
plz you help about Que paper of mahagenco previous your,any model paper relad to it{maharastra power genration}
How to calibrate a orifice differential pressure flow transmitter in process?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)