What should be the ideal tapping location for pressure
differential transmitter for liquid service. If the tapping
taken from the top of the pipe then PDIT will work properly
or not. If PDIT do not work properly then what minimum
corrective action should be taken in order to solve wrong
tapping locations.
Answer / nilesh
1.Ideal tapping location for liquid flow transmitter
orifice tapping in horizontal line is horizontalplane or 45
Degree downwards.
2.If tapping taken from top of the pipe then gases in
liquid service can disturb the measurement and hence
control.
3.Tamperory solution for fluctuation is frequent flushing.
| Is This Answer Correct ? | 4 Yes | 0 No |
what is the diffrence between LCN and UCN
What is Erosion in a control valve?
How process line mpm calculation is done?
How to calculate mmwc values into tonnes?
how to calibrate any tansmiter by loop or hart calibrator
what is temperature compensation?
How does a redundant controller comes in line when the main controller fails??
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
in a electronic controller why we are using 250 ohm resistance in input signal?is i/p is necessary in control valve when we are using electronic controller give details?
What is the difference bitween control net scaner and device net scaner
How to Calibrate the magnetic flow meter on site ?
Why do we floating DC in DC system.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)