11 kv metering is done in my factory.Meter show PF 1.000
but kvarh lag&lead show 24&94 respectively & Avg.PF
is .956 .? is what i do for inproove my PF to 1.000
Answers were Sorted based on User's Feedback
Answer / vinit patil
Your Meter reads Power factor at load center. In your case
load center might be far away from your tariff meter. Since
your APFC meter shows PF 1.00 but at your tariff meter on
11 KV side p.f still lagging. This happens because of
transformer inductance. Add 10 % KVAR of transformer
capacity directly in ON position. Your problem will go out.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / prasad
If your metering cubicle is showing PF as unity then what
is the problem?
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / arvind
it is very difficult to achive 1 power factor because it
depends on the load. as u said it is 0.956, then it is good
that power factor is almost to 1.
| Is This Answer Correct ? | 0 Yes | 4 No |
sir i am pradeep singh from electrical branch and i want to place in software industry(tcs)but i dont know much about programmig languages like c c++.so how can i get a placement in software industry?
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
Why DG self motor winding burnt out?
wat is the role of reactive power in power generation?why we have maintain it.
what is the voltage rating of chiller unit sensors
Give some differences between open loop and closed loop control systems.
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
Star & delta kis principale pa hai.
What are the advantages of a three-phase system over a single-phase system?
Is there any capacitor in 3-phase IM?why,xplain.
In all analog voltmeters or ammeter showing some small size symbols. as well as a star and in star 2no. digit, resister symbol,and other. what is that's meaning ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)