11 kv metering is done in my factory.Meter show PF 1.000
but kvarh lag&lead show 24&94 respectively & Avg.PF
is .956 .? is what i do for inproove my PF to 1.000
Answers were Sorted based on User's Feedback
Answer / vinit patil
Your Meter reads Power factor at load center. In your case
load center might be far away from your tariff meter. Since
your APFC meter shows PF 1.00 but at your tariff meter on
11 KV side p.f still lagging. This happens because of
transformer inductance. Add 10 % KVAR of transformer
capacity directly in ON position. Your problem will go out.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / prasad
If your metering cubicle is showing PF as unity then what
is the problem?
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / arvind
it is very difficult to achive 1 power factor because it
depends on the load. as u said it is 0.956, then it is good
that power factor is almost to 1.
| Is This Answer Correct ? | 0 Yes | 4 No |
Is HT capacitor rating connected directly to motor terminals , related to motor no load current?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
An input device is interfaced with Intel 8085A microprocessor as memory mapped I/O.The address of the device is 2500H.In order to input data from the device to accumulator,the sequence of instruction will be
why insulators colour is BROWN?
What is the difference between "Earthing" and "Neutral"?
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
what are eddy currents
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
why single CT used in DOL starter power circuit?
what is meant by trivector meter?
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)