Explain " FAIL SAFE " feature in temp. measurement.
The fail-safe feature in temperature measurement uses some means to detect an open circuit in the sensor input wiring. An open circuit could be a broken wire, loose connection or a failed sensor.
Should an open circuit be detected, the output signal representing temperature will drive either full scale up usually to a value higher than 20.0mA or full scale down to a value lower than 4.0mA in order to flag, alarm or indicate a failed input circuit.
The failsafe feature and setup for upscale or downscale under fault conditions is sometimes referred to as "thermocouple break". In heating applications, upscale break is usually chosen because an indicated very high temperature on a controller's input will drive a controller's output down to 0% output (assuming reverse control action), preventing an overheat, fire or potential damage situation.
Some failures, such as a shorted thermocouple extension wire or sensor drift can not be detected in with open circuit detection.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
How earthing can be checked????
It is desired to reduce effect of 50Hz pick up in a thermocouple measurement. If a third order LP filter is used for this, what should be its cut off frequency, if gain should be 0.001 at 50Hz.
Which Signal hart communicator work? If there any signal change when hart connect while transmitter in line ?
How can i test procedure grounding for CAT-7 cable? Or How can we test procedure CAT-7 Cable Electrically safe?
what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liquid density .73, transmiter fixed on a fractionation colum, under vaccume 10mbar
What is meant by calibration
what is coriolis principle for mass flowmeter?
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
what are the programming languages used in dcs
How does your previous experience relate to the job you are applying for ?
what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)