what is procedure of calibration of remote seal
transmiter, botom to top flanch 850mm, fluid liquid
density .73, transmiter fixed on a fractionation colum,
under vaccume 10mbar
Answers were Sorted based on User's Feedback
Answer / yomama
Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter
In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5
| Is This Answer Correct ? | 1 Yes | 0 No |
If you installed the remote seal transmitter at flanges,
then in case empty tank /vessel, the transmitter will
showing -mA. so do the followings:
1. Make transmitter 4 mA in this case(without any pressure,
only lower low leg remote seal pressure acting)
2. Apply 850 x 0.73 =620.5 mm of water to high side of
transmitter flange and set transmitter out put 20 mA.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yomama
Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter
In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ys
close the both hp and lp iso valve(so that any pressure
should not act on tx diaphragm). now measure the input
pressure in mm by connecting hand communicator to tx.. this
is the LRV.now measure span(ie here it is 850mm).multiply
span with liquid density(ie 850*0.73).we will get 620.5.
this is your URV
| Is This Answer Correct ? | 0 Yes | 0 No |
3. Differentiate between ultrasonic flowmeter and radar type flow meter.
I want to apply for the universities in US,but i got the GRE score of (650+300=950)TOEFL 69/120.Is this score sufficient for applying universities please i am married i need to go to US because my husband didn't get H1 yet.please send me suggestion
Transmitter reading is zero but in DCS showing one Bar what is the reason ?
how to online calibration of remote seal tx.
what is the reason while warning lamp is on while the engine is cranking?
what is dedband in instrumentation ?
what is the difference between sinking and sourcing inputs and also what are there applications?
I am teja. I am studying Msc(tech) Electronics and Instrumentation (3years course) in Andhra university. But my course is not recognised by UGC and AICTE. Please tell me the job opportunities after this course. And i fineshed PLC course in IGIAT ,Vizag.Also complted my short term coure in SCADA, Seimans WinCC in ATI,Hyd.After Msc can i join Mtech for good job? or phd. How i can get good job in INdustrial Automation Side. Please give replay.Because this is my life matter.
hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection
how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.
WHY WE WILL USE 0-24VdC IN ELECTRONIC CIRCUITS AND INSTRUMENTATION TRANSMITTERS?
3 Answers Aban Power, Jindal, JSW, Sugar Factory,
What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)