Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is procedure of calibration of remote seal
transmiter, botom to top flanch 850mm, fluid liquid
density .73, transmiter fixed on a fractionation colum,
under vaccume 10mbar

Answers were Sorted based on User's Feedback



what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liqu..

Answer / yomama

Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter

In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5

Is This Answer Correct ?    1 Yes 0 No

what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liqu..

Answer / aftab ahmed mazari

If you installed the remote seal transmitter at flanges,
then in case empty tank /vessel, the transmitter will
showing -mA. so do the followings:
1. Make transmitter 4 mA in this case(without any pressure,
only lower low leg remote seal pressure acting)
2. Apply 850 x 0.73 =620.5 mm of water to high side of
transmitter flange and set transmitter out put 20 mA.
aftabmazari@yahoo.com

Is This Answer Correct ?    1 Yes 0 No

what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liqu..

Answer / yomama

Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter

In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5

Is This Answer Correct ?    0 Yes 0 No

what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liqu..

Answer / ys

close the both hp and lp iso valve(so that any pressure
should not act on tx diaphragm). now measure the input
pressure in mm by connecting hand communicator to tx.. this
is the LRV.now measure span(ie here it is 850mm).multiply
span with liquid density(ie 850*0.73).we will get 620.5.
this is your URV

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),

0 Answers  


what is diff between the centrifugal and reciprocating

2 Answers  


Difference between dcs and plc including date processing and architecture.

0 Answers  


why direct mounted pressure transmitters is always installed with DBB ( double bleed block) valve in process line or top of the tanks ?

0 Answers  


For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?

2 Answers   NA,


why do 4 mA serves as 0% not 0 mA?

10 Answers  


What is the Difference between PE,IE and ISE

2 Answers  


A flange is used for instrument connection for a system with a design temperature of 316&#61616;C (600&#61616;F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer

0 Answers  


Can anybody tell me application of PLC,DCS,SCADA.

3 Answers   Reliance,


I am teja. I am studying Msc(tech) Electronics and Instrumentation (3years course) in Andhra university. But my course is not recognised by UGC and AICTE. Please tell me the job opportunities after this course. And i fineshed PLC course in IGIAT ,Vizag.Also complted my short term coure in SCADA, Seimans WinCC in ATI,Hyd.After Msc can i join Mtech for good job? or phd. How i can get good job in INdustrial Automation Side. Please give replay.Because this is my life matter.

0 Answers  


How we can check the 2 wire proxy switch? & how it is connected to DI MODULE OF PLC?

0 Answers  


What is wet leg condition and why is it used?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)