My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
Answer / carl_ellis
Any 2 wire, loop powered 4-20mA transmitter that puts out
30mA is broken. The only transmitter that puts out 30mA is
a legacy 10-50mA transmitter from 20-30 years ago.
While the upper end of the 4-20mA signal range is 20.0mA,
most 2 wire, loop powered transmitters allow for some slight
signal over-range, typically 20.5mA.
NAMUR standards use 21.0 mA to signal a fault or failure
mode. Other vendors use other values, 20.8mA, 21.2mA or
some value in the range of 21mA. But no vendor uses 30mA
as a fault mode.
The transmitter is broken or dysfunctional.
Carl Ellis
Measure First
Is This Answer Correct ? | 5 Yes | 0 No |
what is span adjusment of transmitter? what is the function of positioner/
what will be the output of the temparature transmitter if temp is 120 degre celcius.
1 Answers Base Automation, NTPC, PDO,
WHAT IS THE DIFF. BETWEEN SKIN TEMPERATURE AND PASSES TEMPERATURE..?
how to relay switch sense the fault?
Which are all the commonly used Bordon tubes in the pressure gauges. Do any one use ASTM A 312 tubes for this purpose?
Dear Sir/Madam, I am attending an interview for ETs in BHEL. I have cleared my written test under Electronics (Instrumentation). This is the first time I am appearing for an interview. Can any one who has attended the interview earlier give me a clue to face the interview. With regards Sindhu
how to calibrate any tansmiter by loop or hart calibrator
the output of the common trasmitter protocol in qatar gas are the following
if i change range of flow transmitter in th field then does it need to change range in dcs?
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
what is difference b/w tube and pipe ?
6 Answers BSL, Descon, Kirloskar,