My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
Answer / carl_ellis
Any 2 wire, loop powered 4-20mA transmitter that puts out
30mA is broken. The only transmitter that puts out 30mA is
a legacy 10-50mA transmitter from 20-30 years ago.
While the upper end of the 4-20mA signal range is 20.0mA,
most 2 wire, loop powered transmitters allow for some slight
signal over-range, typically 20.5mA.
NAMUR standards use 21.0 mA to signal a fault or failure
mode. Other vendors use other values, 20.8mA, 21.2mA or
some value in the range of 21mA. But no vendor uses 30mA
as a fault mode.
The transmitter is broken or dysfunctional.
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
why we connect digital multimeter in series for dc current measurement and parallel for dc voltage measurement.
how to do dynolab wind speed sensor loop test, how to simulate value,i have simulate mA 4-20mA but not responding in DCS faceplate, please kindly advice me any one.
how to know the URL and LRL for steam drum level and why the calibration range is in negative ?
how to calibrate transmitter online (in running plant)please explain correct procedure
why micro controller 8051/52's clock frequency is internally divide by 12 ?? and why it is further divide by 32 in UART serial communication ??
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
It is desired to reduce effect of 50Hz pick up in a thermocouple measurement. If a third order LP filter is used for this, what should be its cut off frequency, if gain should be 0.001 at 50Hz.
what is the basic principal of vertax flow meter
3 Answers Balrampur Chini Mill, Saba,
how commission a transmitter evev plant is already running
how to calculate static pressure in a pipe line,when we know the DP(differential pressure) in the line, area of the pipe? please any one tell me the relation between them..?
Why using negative voltage in vibration measurement?
what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)