It is desired to reduce effect of 50Hz pick up in a
thermocouple measurement. If a third order LP filter is
used for this, what should be its cut off frequency, if
gain should be 0.001 at 50Hz.
Answer / guest
5Hz.This has a -20dB/decade fall off. the required gain is
0.001 or -60dB.Being third order filter, cut off frequency
should be 50/10 = 5Hz
| Is This Answer Correct ? | 0 Yes | 0 No |
How to adjust the zero & span of a control valve from the posiitioner(MIL)?
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
What is the electronic transmitter frequency.
What is the differaence between PLC and DCS?
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
can we control operation of PLC from operator station?
how to connect transmitter measuring sulfur process? 1-by using long impulse line or 2- by using coated short impulse line
What are the interlocks we have to check during the start up of LP/HP compressor?
what is the principle of vibration
what is the function of boiler in plant?
WHY WE WILL USE 0-24VdC IN ELECTRONIC CIRCUITS AND INSTRUMENTATION TRANSMITTERS?
3 Answers Aban Power, Jindal, JSW, Sugar Factory,
Full form of KKS when use DCS.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)