Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.pls help me
Answer / carl_ellis
An offset in readings from separate RTD's can indicate
- a difference in calibration of the analog input devices
- a bad RTD element, one that has drifted out of spec
- a common ground issue with ground loops between the analog
input devices
An RTD is supposed to be ungrounded and the two RTD's in a
duplex element are supposed to be electrically isolated from
one another, so it is unlikely the ground loop is unlikely
unless poor wiring of the extension wire or head wiring has
created a connection to ground.
If you're complaining about a small difference of the
indicated temperatures, then get out your cal gear and cal
the inputs.
To check for a bad RTD, I'd take an ohmmeter and see if any
leg on the A side has any connection to the B side by
disconnecting the wiring from each analog input and check
the resistance. If there's a low resistance, it indicates
some connection from A to B. If the extension wires are
then disconnected and the resistance is checked on the RTD
lead wires and the resistance remains, then it's a bad RTD.
If the resistance goes high (open circuit) then the
extension wire is shorting or making a low resistance
connection somewhere.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 2 No |
Why 1-5 vdc a standard?
1 Answers Process Control Technologies,
Anybody can tell me how to convert mmHg2o /psi to scfm please give me formula of conversion
what is instrument termination
What is voltage regulator?
what is difference between PLC and DCS?
What is the difference between uv and ir scanners? and what is the workig principle of both
What skill/s does the Instrument Technician has?
What are the difference between mass flow meter, magnetic flow meter and vortex flow meter.
list of flame proof certification ?
what is buoyancy law?
why to use 3 wire at RTD ? what's the reason for common wire ?
what is a device net.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)