Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why using 4-20ma not using 0-20or why not using 1-
20ma???????

Answers were Sorted based on User's Feedback



why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / chandrasekarapandian

4-20 mA is the universal standard.
Justification:
1. easily splittable ranges 0 % = 4mA
25 % = 8mA
50 % = 12mA
75 % = 16mA
100 % = 20mA
2. 4 to 20 mA passed over 250 ohms coil resistance will
produce a suitable voltage sourcew of 1 to 5 volt.
3. LIVE ZERO
If our sensor to PLC wire connecton is open PLC reads 0mA
where as if the input of sensor in ZERo PLC reads 4mA.

Is This Answer Correct ?    14 Yes 3 No

why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / srinivasan narayanan

Most of the Transmitters output used 4 -20mA. This is because to identify whether the transmitters are live or not

if the Transmitter shows 4 mA it's a live Zero

if the Transmitter Shows 0 mA it's a Dead Zero

Is This Answer Correct ?    6 Yes 1 No

why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / seshu

when we are using 0 to20ma if any case cable is damage it
carry o ma signal continues so we are using 4 to20 ma

Is This Answer Correct ?    5 Yes 1 No

why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / kalpit thakkar

Instrument has own Load of 3mA. so we go for 4-20mA. & Also IEC Approved to 4-20 mA.

Is This Answer Correct ?    0 Yes 0 No

why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / rathod mukesh

0 - 20 ma range is not use in the instrumentaion as standard range because if we use 0 ma for zero process parameter value, if any reason loop wire become break although plc or micro controller get 0 Value at unkown process parameter value and its understand process is in healthy condition but actcully fault is occur in physical data(0-20 ma) transmission link . the plc or micro controller is not accept proper value of process prameter. And we cant define live zero of process parameter. Use to 4- 20 rane ma we easily define live zero.

Is This Answer Correct ?    0 Yes 0 No

why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / rathod mukesh r

If we use 0 - 20 ma rage as standard then we cant define live zero .

Is This Answer Correct ?    0 Yes 0 No

why using 4-20ma not using 0-20or why not using 1- 20ma???????..

Answer / nilesh

This is a universal standard adopted.4 mA at 0% ensure live
zero.

Is This Answer Correct ?    5 Yes 7 No

Post New Answer

More Instrumentation Interview Questions

Which boiler is use in power plant

1 Answers   Jindal,


How to force the bit in GE Mark V?

1 Answers  


what is meant by calibration

3 Answers  


WHAT IS THIS INSTRUMENTATION?

7 Answers  


Explain about the leakage class of the control valves

0 Answers   CCIE,


if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount

3 Answers   Baumer,


In Safe Guarding test what means by "Failed to Danger" ?

0 Answers   Optimal,


Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?

1 Answers   Siemens,


What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why

2 Answers  


what is pt100 RTD, and does 100 stands for

8 Answers   Tata Power,


What is Positive Calibration and Negative Calibration?

0 Answers   SA Kent,


What is the reason for not giving very High Proportional Gain Kp in PID Controller?

2 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)