why using 4-20ma not using 0-20or why not using 1-
20ma???????
Answers were Sorted based on User's Feedback
Answer / chandrasekarapandian
4-20 mA is the universal standard.
Justification:
1. easily splittable ranges 0 % = 4mA
25 % = 8mA
50 % = 12mA
75 % = 16mA
100 % = 20mA
2. 4 to 20 mA passed over 250 ohms coil resistance will
produce a suitable voltage sourcew of 1 to 5 volt.
3. LIVE ZERO
If our sensor to PLC wire connecton is open PLC reads 0mA
where as if the input of sensor in ZERo PLC reads 4mA.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / srinivasan narayanan
Most of the Transmitters output used 4 -20mA. This is because to identify whether the transmitters are live or not
if the Transmitter shows 4 mA it's a live Zero
if the Transmitter Shows 0 mA it's a Dead Zero
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / seshu
when we are using 0 to20ma if any case cable is damage it
carry o ma signal continues so we are using 4 to20 ma
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kalpit thakkar
Instrument has own Load of 3mA. so we go for 4-20mA. & Also IEC Approved to 4-20 mA.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rathod mukesh
0 - 20 ma range is not use in the instrumentaion as standard range because if we use 0 ma for zero process parameter value, if any reason loop wire become break although plc or micro controller get 0 Value at unkown process parameter value and its understand process is in healthy condition but actcully fault is occur in physical data(0-20 ma) transmission link . the plc or micro controller is not accept proper value of process prameter. And we cant define live zero of process parameter. Use to 4- 20 rane ma we easily define live zero.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rathod mukesh r
If we use 0 - 20 ma rage as standard then we cant define live zero .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nilesh
This is a universal standard adopted.4 mA at 0% ensure live
zero.
| Is This Answer Correct ? | 5 Yes | 7 No |
I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow measurement so whats the formula.
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
Describe how to use megger to measure the earth resistance and insulation resistance
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
Could anybody pls give ans of boiler 3 element control system?
How we can check the 2 wire proxy switch? & how it is connected to DI MODULE OF PLC?
What is furnace draft control?
which one is best profibus or RS485 for communication?
How to calibrate electronic type level switch low?
Which boiler is use in power plant
what is the criteria to decide conductor size of a cable ?
Calibration of flow transmitter.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)