what is the difference between E/P positioner and I/P
positioner in control valve , in which application the
respective positioner are used in.
Answer / carl_ellis
An E/P converter is a voltage to pressure transducer; it
converts 0-10Vdc to 3-15 psi
An I/P converter is a current to pressure transducer; it
converts 4-20ma to 3-15 psi
Either is used to convert an electrical control signal to a
pressure control signal, typically for a valve positioner or
sometimes a valve actuator.
Current signals are the vast majority of signals in the
process world.
Voltage signals tend to be used in machinery or in a
laboratory, because of the voltage loss over long distances
and tendency to pick up noise more than current signals.
The appropriate I/P or E/P transducer is determined by which
electrical signal is in use.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 1 No |
when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICATOR.
Operational amplifiers
There is a problem with our HART475 it is not communicating with smart devices error becomes "NO DEVICE FOUND"we have insert 250ohm resistance as per requirement but invain plz tell me the solution?
Q1: Consider part of a control loop, which excludes the transmitter, consisting of a process, a controller and a control valve which may be represented by two dead times of 0.5 min each and three exponential lags of 0.8 min., 1.0 min. and 1.5 min. respectively. We wish to express this system as an overall first order plus dead time (FOPLD) model ie gain, time constant and process dead time. (We will see later that this is often done, to simplify controller tuning). For this exercise, gain is considered to be 1.0. (A) If the transmitter is a flow transmitter whose behaviour can be described by a dead time of 0.2 min. and an exponential lag of 0.5 min. in terms of the overall dead time and overall first order lag how can the system behaviour be approximated ? Overall dead time = Overall time constant = (B) If the transmitter is a temperature transmitter with a temperature sensor in a protecting well whose behaviour can be described by a dead time of 0.7 min. and an exponential lag of 15 min. how can the overall system behaviour be approximated now? Overall dead time = Overall time constant =
Why Bently Nevada use negative voltage for vibration probes?
Why the Proximitor supply should be Negative voltage? Why should not we give Positive voltage to the Transducer?
What are the different type of instrument used in cement industry with uses
how to convert bar to mA?
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
Can anyone help me with the Question bank(objective type) for complete Instrumentation engineering,either a soft copy or a Hard copy(Book),or the name of the author ,or publisher.
what is basic working principle of Governer in power plant?
Why all the drains(Gland sealing,ESV,Casing inlet etc) are directly connected to the flash tank instead of hotwell of the condensor in the power plant? My Email Id:naba02222@gmail.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)