My ups output shows 230 v between phase and neutral,but show
zero between phase and earth.Is the system/installation is
correct.If not what will be the possible reasons
Answers were Sorted based on User's Feedback
Answer / nck
correct.it will show output between phase and earth only and only in faulty condition not in normal.if there is fault and still not output between ph-earth then your earthing is not properly done.
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / hemalatha
earthing point where you checked may not be perfect.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / akot
there should be out put between phase and earth unless the
earth is also having current or improperly done, to rule
out if your earth is having current measure earth to
neutral.
| Is This Answer Correct ? | 0 Yes | 2 No |
can we use engine degreaser for electrical motors?
what is resistor
what is surge impedance loading?
What is sensitivity of a measurement?
why do we earth the tandelta point of a power transformer bushing?
What is meant by "tampering detection" of a electrical energy meter?
why we used to transmitt the power at higher voltage why not at lower voltage
What is the starting current of a DC Motor?
Is Indian railway uses 25000v ac or dc?
What is the rating of your substation and what are the different types of substations?
what is meant by negative conductor?
What is the main difference b/t Earth leakage relay & Earth fault relay.I want protect my LT panel(Distribution Panels)which relay have to propose.......
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)