My ups output shows 230 v between phase and neutral,but show
zero between phase and earth.Is the system/installation is
correct.If not what will be the possible reasons
Answers were Sorted based on User's Feedback
Answer / nck
correct.it will show output between phase and earth only and only in faulty condition not in normal.if there is fault and still not output between ph-earth then your earthing is not properly done.
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / hemalatha
earthing point where you checked may not be perfect.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / akot
there should be out put between phase and earth unless the
earth is also having current or improperly done, to rule
out if your earth is having current measure earth to
neutral.
| Is This Answer Correct ? | 0 Yes | 2 No |
what are the types of control panel used in industries & all electrical purpose ?
What is current divider rule (cdr)?
Which fault is caused by lightening and thuderstorm a. Line to line fault b. Single line to ground fault c. Double line to ground fault
how electronic energy meter works?
difference between slippring induction motor and Generator?
1.Whats the use of GNAC(Generator Neutral Accessory Compartment) 2. why generator or any other system require Neutral Grounding and not Phase grounding 3. what happens if any one of the phase is grounded. 4. if 15kv is grounded directly what will happen, why it should not be grounded like that 5. use of of NGTR(Neutral Grounding Transformer and Resistor) for grounding is helpfull and how
5 Answers BEMCO, CSS, Powergear,
how to check the insulation for motor using megger?
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts same result on 24Volts and with ground 12Volts only expert answer that thanks we can not ground the battery.
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
acsr dog conductor specification
Wghat is D-curve MCBs
In a three-phase full converter, every SCR conducts for a.60deg. b. 120deg. C.180deg. d.90deg
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)