Please explain the difference between instrument range and
calibration range in terms of pressure transmitter?
line design pressure: 93 bar
operating pressure : 82 bar
press Transmitter Range?
calibration range ?
Answers were Sorted based on User's Feedback
Answer / ahmed helmy
- instrument range is the maximum range of instrument.
- Calibration range is at which the instrument calibrated
for example
- if we have a pressure tx instrument range 0:10 bar
- we can calibrate it at any position between 0:10 bar suppose we calibrate it at 0:4 bar its mean its calibration range
is 0:4bar and instrument range 0:10 bar
Based on your case:
- line design pressure=93 bar (max pressure in the line)
- operating pressure=82 bar
so we can install pressure tx range:0 to 120 bar and calibrate the pressure tx in range from 0 to 93 bar
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / furqan
In addition we also can not calibrate the pressure transmitter as equal to designed line pressure
calibrate the pressure transmitter on 80 percent of designed line pressure.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sri
hi can i know y reasons why cant we choose instrument range as a calibrated range?
| Is This Answer Correct ? | 0 Yes | 1 No |
I am teja. I am studying Msc(tech) Electronics and Instrumentation (3years course) in Andhra university. But my course is not recognised by UGC and AICTE. Please tell me the job opportunities after this course. And i fineshed PLC course in IGIAT ,Vizag.Also complted my short term coure in SCADA, Seimans WinCC in ATI,Hyd.After Msc can i join Mtech for good job? or phd. How i can get good job in INdustrial Automation Side. Please give replay.Because this is my life matter.
I am new in work for 1 of our project we have some instrument in BOM including Pressure, Temp. and so on, I also noticed some objects like pressure switch process HOOK UP; which I don't know what does "HOOK UP" mean here.
I HAVE PRESSURE TRANSMITTER WITH TWO WIRES 24 VOLTS SUPPLY.IF TRANSMITTER WILL GIVE SIGNAL TO THE DCS WHAT HAPPEN TO THE 24 VOLTS POWER SUPPLY IT WILL DROP OR REMAIN TO 24 VOLTS POWER SUPPLY.
pressure switch range 0 to 2bar.i have to install from ground level to 5 meters height.what is the formula the to increse the range ? and every 1 meter how much pressure should be add ?
what is the meaning of wet leg & where is it used?
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
We are used CENTUM CS3000 of YOKOGAWA. please tell me how to simulate wihtout FCS and vnet.
why we use 24v dc in instrument rahter than 230vac????
Draw a 3 element level control loop and explain
can you provide me full detail about instrumentation in ONGC??
Is there a particular problem if two proposals from the same observatory (originating with different partners) are submitted?
What is the differerence between hysterisis and linearity.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)