Please explain the difference between instrument range and
calibration range in terms of pressure transmitter?
line design pressure: 93 bar
operating pressure : 82 bar
press Transmitter Range?
calibration range ?
Answers were Sorted based on User's Feedback
Answer / ahmed helmy
- instrument range is the maximum range of instrument.
- Calibration range is at which the instrument calibrated
for example
- if we have a pressure tx instrument range 0:10 bar
- we can calibrate it at any position between 0:10 bar suppose we calibrate it at 0:4 bar its mean its calibration range
is 0:4bar and instrument range 0:10 bar
Based on your case:
- line design pressure=93 bar (max pressure in the line)
- operating pressure=82 bar
so we can install pressure tx range:0 to 120 bar and calibrate the pressure tx in range from 0 to 93 bar
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / furqan
In addition we also can not calibrate the pressure transmitter as equal to designed line pressure
calibrate the pressure transmitter on 80 percent of designed line pressure.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sri
hi can i know y reasons why cant we choose instrument range as a calibrated range?
| Is This Answer Correct ? | 0 Yes | 1 No |
i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me
How to calibrate H2s Dectector
What is difference between reset and initialization in system.
How to calibrate vertex flow meter? How to calibrate mass flow meter?
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
can we create an interrupt in plc through scada?
How to calibration of vibration probe
1 Answers Mina Al Ahmadi Refinery,
can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.
what type of cables are used for f&G systems and detectors, what is the standard colour?
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
How does work A temperature valve or fv control valve in process plz brief me
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)