In Transformer testing at Shop test we normally test for
vector group, open ckt.,short ckt. but what are the other
test performed for transformer once it reaches at site.For
e.g:if the transformer is dry having rating 1000KVA?
Answers were Sorted based on User's Feedback
Answer / guest
1. Insulation Resistance Measurement
a . For LT systems, use only 500V or 1000V Megger
b. For MV & HV systems, use 2500V or 5000V Megger
c. Remove Earth from Transformer neutral
2. Winding Resistance Measurement
R-N AND r-n
Y-N y-n
B-N b-n
3. Magnetic Current Test
Applied Voltage : RY YB BR
Measured Current : R Y B
4. Magnetic Balance Test
5. Vector Group Confirmation.
6 . Short Circuit Test and Differential Stability.
7 . REF Stability Test
8. Cooler Circuits.
9. Auxilliary Protection Circuits
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / brahma
Also Double voltage double frequency, if customer ask impulse
Is This Answer Correct ? | 0 Yes | 0 No |
hello friends..... any one have papers or any study materials?sail ,hpcl...?
what is difference between window type and wound type transformers?where we will use window type and wound type transformers?
what is the purpose of reactor in electrical substations ?
How single phase & 3 phase motor select rotating direction ie clockwise/anticlockwise
how to calculate restraing current and operating current for differential protection if 20 mva transformer is OLTC 33 kv/11 kv ? and what should be the type and ratio of CT?
when we have to purchase the transformer by own i.e how much load will preferred HT connection?
when a motor is connected in parallel with the existing motor the pf will change or not?
how do you find making current and breaking current of the circuit breaker
What are the advantages of speed control using thyrister?
How can we determine or find out the proper size of any cable if nothing is mentioned on it.Calculation of size in Sq.mm???
what is thresold of perception
what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load