you have a 2 tonne ac that operates for 2 hrs daily what will
be you monthly bill (this is complete question asked nothing
else was given)?
Answer / sagar parekh
1 ton = 12000 btu/hr
= 12000*0.0003929
= 4.175 hp
= 3.5 kw
total hrs of month= 60 hr
kwh=3.5*60=210 units
suppose tariff is 3rupee per unit so final ans. is 630 rupee
Is This Answer Correct ? | 3 Yes | 0 No |
I WOULD LIKE NOW WHY WE CANT USE SOME CT FOR MESARING AND PROTECTION
Suppose a 3 phase, 2 pole, 440V induction motor is driving a flywheel of 600mm diameter, 150kg mass. By using v-belt and pulley, the speed is increased to 4500 RPM. What will be the effect on motor current?
Why in medium voltage system(3.3kv to 33kv, neutral is earthed with either resistance, reactance or neutral grounding resistance?
what is gridrotor resistance starter
What is EOL?
what are the difference between PLC and embedded
what is the voltages using in movie theaters??? why ??why not other??
why choke is provided in the centre of the tube light?
When should I use earth leakage circuit breaker for incomer and when should I use it for each feeder seperately?
Then what do you call a transformer that is installed on the ground?"
how to get more than 1000 ohms between 2 earth pits ?
What is PEC??Applications........