why in three phase 440 circuit in all phase current is
almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i
check with clamp meter it shows 25 A?
Answers were Sorted based on User's Feedback
Answer / kiran
Principle is vector summation.
Ir + Iy + Ib = 0
and not arithmatic summation.
Since neutral current is substantial 25A, the three RYB
vectors are not 120 degree apart. Means powewr factor in
each phase differs drastically. Thats why though there is
no much difference in RYB current, neutral has substantial
current.
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / amit
In balance condition neutral current is zero. Flux in all
three phases are in addative nature.
flux in R + flux in Y + flux in B = 0(zero)
but in your case it is different because of differnt
currnet in phases, which will affect and cause a unbalance
condition, will produce a flux in neutral and current
flowing through neutral. But in your case it is 25A which
is to much unbalance condition.
Take once again reading.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / rajesh siwach
valve of currents and voltages depend upon the manner in
which the 3 phase system connected,either in star
connection or in delta connection
| Is This Answer Correct ? | 1 Yes | 4 No |
what is harmonics?
what is meant by peak load
HOW THE AC GENARATOR CAN GENARATE REACTIVE POWER,HOW CAN WE CONTROL IT.AND OTHER SOURSES OF REACTIVE POWER GENARATIONS ARE WHAT.
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
Why (In India) we preferably go for +-30 deg connection of transformer? what are the advantages in this connection?
Why X'mer rating in kva only?
Our Company's Contract Demand is 110 kVA. We use 12 Capacitors each of 12.5 kVAr Capacity to maintain Power Factor of 0.99. So, what steps should we take so that our Contract demand does not exceed 110 kVA?
I WOULD LIKE NOW WHY WE CANT USE SOME CT FOR MESARING AND PROTECTION
we have 15 ampere variyac but we want 30 ampere variyac what we do
what is alternater?
What is the drawback of static coefficients?
In a Tap changing transformer where is the tap connected , is it connected in the primary side or it is connected in secondary side
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)