I have flow transmiter DP range is 0 to
5000mmwc,(convert) Display to be show in
m3/Hr.
Answers were Sorted based on User's Feedback
Answer / sajid ali khan
Dear the Flow range is not just a function of the flow
transmitter. It is function of the Flow Element, that can
be an Orifice or a venturi, etc.
You have to know the Flow calculations and then calculate
the relationship of dp vs flow
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sivaram
Dear bro.In flow calculation Need Design DP and Q Parameters,Then configure range DP ,out put function Sq root display range configure Given Q,Simple you will get Exact
flow
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kirubakaran
example:
50% range =squareroot of(d.p/max-min)
50/100 = square root of(dp/5000-0)
take square on both side
2500*5000/10000= d.p(differential pressure)
1250mmwc= d.p
similiarly find 0%,25%,75%,100% this is for square root output
pls see range in dcs example 0-50ton
then put corresponding value
range o/p(ma) mmwc tons
0% 4 0 0
25% 8 312.5 12.5
50% 12 1250 25
75% 16 2812.5 37.5
100% 20 5000 50
if u feel correct means follow this
| Is This Answer Correct ? | 3 Yes | 6 No |
what is pneumatic control system?
What are the problems faced while testing HART instruments?
y v r connecting 250 ohms resistor in series when u cummunicate with BT in bench calibration?
WHAT IS THIS INSTRUMENTATION?
Someone please do mail me some instrumentation questions for Hindustan Petroleum test to avinalexander@gmail.com .Really would be gateful if someone could help me
3 Answers HPCL, Immersion, IOCL,
An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?
What is cold junction compensation in thermocouples? How is it achieved?
how to install the Ph and Conductivity analyser? is there are any procedures which has to be maintained.
What unit is used for measuring comp. outlet flow. it is CFM, M3/hr or NM3/hr. ?
How would i calibrate a new commissioned flow transmitter???
Please send the all question with answer related for interview.
What is the diffrence between digital signal processing and discrete signal processing?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)