what are the documentation and instrument identification system used to identify the correct device to be calibrated? name atleast three.
Answer / carl_ellis
- P&ID: tag name/number for the instrument in question,
but not the location
- Loop diagram shows tag name/number, has a location
description (field, panel, I/O rack, control room) and
wiring terminals ID (are wires 1578 and 1579 connected to
the instrument in question?)
- ISA's instrument spec sheet has a section for calibration
with input/output, but more importantly, the following
section has Component Identification by manufacturer and
model number. The serial number isn't there because this
document defines the functionality, not a specific device.
- The company's "Instrument Specification Data Form" should
have a field for a location and instrument serial number
- Calibration data sheet should have a field
for "Location", tag and serial number.
- There should be a stainless tag on a field instrument
- The handheld communicator displays the tag name when
connected. The instrument's tag name should match the work
order's tag.
- The local "Calibration status label" on or inside the
instrument always has a tag ID.
Carl Ellis
Measure First
| Is This Answer Correct ? | 7 Yes | 0 No |
principle of automatic votage regulator
why can't we use 5-20mA standard or some other instead of 4- 20mA?
i want know about capillary type LT transmitter installation. we can install any location in between to HP and LP leg?
where proximity sensor installed on tank in loading arm application
HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY IT IS USED ON ESD ON OFF VALVES?
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...
What is difference between radial vibration and axial vibration explain in detail .
I have flow transmiter DP range is 0 to 5000mmwc,(convert) Display to be show in m3/Hr.
Someone Please tell me what are the Pre-Commissioning activities in a Thermal Power Plant for an instrumentaion Engg.
Calibration procedure for water rotameters
Draw a 3 element level control loop and explain
What is the calibration procedure of Drum level transmitter if range is 0 to -400 mmh2o in lab?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)